    City Multi pipe sizing problem



    Hey!

    I'm project managing on a project where we have installed 2 City Multi systems i.e. PURY-P300YHM-A outdoor units each connected to a master BC box and 1 slave BC box. The pipework between the outdoor units and the master BC boxes should be 7/8 & 3/4 but the pipe installer has somehow managed to install both gas and liquid with 7/8 on both systems! The pipe run is approx 30m total but the last 5m to the outdoor units are not finished so we can do this bit with the correct pipe sizes.. Before i start frantically changing both the liquid lines down to 3/4 (a big job!) i was wondering if anyone can give me some advice/thoughts on whether it is necessary? All other pipe sizes between BC boxes and to indoor units are correct.

    Thanks in advance!



  2. #2
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: City Multi pipe sizing problem

    To be honest i'm not too sure of the exact implications,however at least the pipe's are not under sized.
    Personally i've never been in your situation.The only advice i could offer would be change the liquid line if at all possible.
    If its not possible the only thing you can do is calculate the additional charge using the figures for a 7/8 liquid line.
    That in itself may cause issues with overcharge faults.
    Do the math for 3/4 and 7/8 liquid lines and weigh up the options, then if its a big difference make an educated guess.
    I dont have a manual to hand to do it myself at the moment but ill have a look around.
    30 mtrs of 3/4 = 30x 0.16=4.8kg of refrigerant
    I cant remember the multiple for 7/8 if you have it do the same and weigh up the difference , it will give you some idea of what to expect.
    Cheers
    Stu
    Last edited by stufus; 09-02-2011 at 05:24 PM.
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  3. #3
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: City Multi pipe sizing problem

    I would rip the 7/8th out and replace it with for 3/4, the pipes are that size for a reason.

    Imagine trying to run it up and having problems with any of the indoors not cooling properly upon commissioning it would be even worse then.

    Just my 2cents.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  4. #4
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: City Multi pipe sizing problem

    I almost forgot , your warranty will be shot as its not installed as per manufacturers specifications.
    As Marc says it's not worth the risk and accompanying grief.
    Cheers
    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  5. #5
    Join Date
    Aug 2009
    Location
    east anglia
    Age
    49
    Posts
    95
    Rep Power
    15

    Re: City Multi pipe sizing problem

    Best practice is as Marc said but it really wont make a differance if you don't change it.
    Stu this is true with warranty but i dont think mitsi would come to site over a compressor
    Regards Croc
    Last edited by croc1774; 09-02-2011 at 06:55 PM.

  6. #6
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: City Multi pipe sizing problem

    to achieve finesse- do th job properly and weigh in all that oversized 7/8-pity they didnt lash in 1 5/8

  7. #7
    Join Date
    Feb 2011
    Location
    england
    Age
    50
    Posts
    10
    Rep Power
    0

    Re: City Multi pipe sizing problem

    If in Doubt read the instructions lol . Yeah always stick with the spec like guys say ! It will only come back to bite you on the derierre ! :-)

  8. #8
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: City Multi pipe sizing problem

    There have been cases over the years when manufactures have specified 1 inch pipe & here in the UK we dont use 1 inch. In this case maunfactures tend to advise use next size up @ 1 1/8.
    R22 replace systems can also operate with larger pipe sizes but there are limits to the pipe lenghs & some impact on system performance depending on the pipe lenght.

    In your case changing from 3/4 to 7/8 is not likely to have a big impact on system performance
    But
    What if there is a problem with the system & you need on site technical support from the manufacturer ?
    A very good chance that you could end up with no warranty & a system not working properly.

    It will be easier to change the pipework now rather than after handover as remedial works.

Similar Threads

  1. Mitsubishi City Multi Heating Problem
    By Contactor in forum Air Conditioning
    Replies: 1
    Last Post: 27-11-2010, 10:07 PM
  2. Mitsubishi G50 / City Multi Control Problem
    By Contactor in forum Air Conditioning
    Replies: 3
    Last Post: 12-11-2010, 08:00 PM
  3. city multi
    By junakw in forum Air Conditioning
    Replies: 1
    Last Post: 01-09-2010, 02:19 PM
  4. R22 Mitsi City Multi problem
    By markj in forum Air Conditioning
    Replies: 10
    Last Post: 05-03-2007, 08:44 AM
  5. r22 city multi problem
    By mr slim in forum Trouble Shooting
    Replies: 3
    Last Post: 11-01-2006, 06:27 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •