Clivet MSAN
Hi, has anyone ever recharged a Clivet MSAN 162 dx system before?
The reason i ask is i've been working on a system that has lost its charge and i don't know what the gas charge is.
The condensor says 6.8kg on it and the manual says for every 10m then add 3.7kg.....the pipe run is 60m but do i need to also add refrigerant for the indoor unit as well which is a large floor standing unit (CNV142)
I've spoke to a guy from Clivet and he didn't know the answer.
The difference between genius and stupidity is that genius has its limits.
Marc
-
08-02-2011, 08:21 PM #2
Re: Clivet MSAN
add the factory charge 6.8kg then add the3.7kg x6=29kg total chage-but check the factory charge may be ok for upto 10mtrs is there a sight glass?
-
08-02-2011, 09:07 PM #3
Re: Clivet MSAN
I asked the guy at Clivet and he seemed to think that i wouldn't need to add the factory charge, just the 3.7kgx6 needed for the pipework which i thought didn't seem right but he admitted that he wasn't sure.
I think the factory charge of 6.8kg must cover the first 10m so maybe need to charge 5x 3.7kg and trim the charge from there.
Yes the indoor does have a sight glass, i'll watch this as i'm charging it.The difference between genius and stupidity is that genius has its limits.
Marc
Similar Threads
-
Clivet versatemp
By redbull in forum Air ConditioningReplies: 1Last Post: 11-12-2010, 06:39 PM -
Just would like to say a big thankyou to Clivet.
By matt p in forum Chit Chat & Service StoriesReplies: 3Last Post: 19-08-2010, 09:10 PM -
Clivet chiller
By philjd26 in forum Air ConditioningReplies: 8Last Post: 21-05-2009, 08:57 AM -
clivet chillers
By bojan501 in forum Air ConditioningReplies: 8Last Post: 17-05-2009, 06:00 PM -
Clivet chiller
By texanul in forum IndustrialReplies: 2Last Post: 14-11-2008, 09:56 PM