Results 1 to 3 of 3

Thread: Clivet MSAN

  1. #1
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Clivet MSAN



    Hi, has anyone ever recharged a Clivet MSAN 162 dx system before?

    The reason i ask is i've been working on a system that has lost its charge and i don't know what the gas charge is.

    The condensor says 6.8kg on it and the manual says for every 10m then add 3.7kg.....the pipe run is 60m but do i need to also add refrigerant for the indoor unit as well which is a large floor standing unit (CNV142)

    I've spoke to a guy from Clivet and he didn't know the answer.


    The difference between genius and stupidity is that genius has its limits.

    Marc

  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Clivet MSAN

    add the factory charge 6.8kg then add the3.7kg x6=29kg total chage-but check the factory charge may be ok for upto 10mtrs is there a sight glass?

  3. #3
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Clivet MSAN

    I asked the guy at Clivet and he seemed to think that i wouldn't need to add the factory charge, just the 3.7kgx6 needed for the pipework which i thought didn't seem right but he admitted that he wasn't sure.

    I think the factory charge of 6.8kg must cover the first 10m so maybe need to charge 5x 3.7kg and trim the charge from there.

    Yes the indoor does have a sight glass, i'll watch this as i'm charging it.
    The difference between genius and stupidity is that genius has its limits.

    Marc

Similar Threads

  1. Clivet versatemp
    By redbull in forum Air Conditioning
    Replies: 1
    Last Post: 11-12-2010, 06:39 PM
  2. Just would like to say a big thankyou to Clivet.
    By matt p in forum Chit Chat & Service Stories
    Replies: 3
    Last Post: 19-08-2010, 09:10 PM
  3. Clivet chiller
    By philjd26 in forum Air Conditioning
    Replies: 8
    Last Post: 21-05-2009, 08:57 AM
  4. clivet chillers
    By bojan501 in forum Air Conditioning
    Replies: 8
    Last Post: 17-05-2009, 06:00 PM
  5. Clivet chiller
    By texanul in forum Industrial
    Replies: 2
    Last Post: 14-11-2008, 09:56 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •