Results 1 to 8 of 8
    Apr 2009
    Qatar
    44
    13
    Urgent help:: Refrigerant oil york alternate
    can i change the YORK E refrigerant Oil for YAEP Chiller Compressor.
    i checked and its not available in QATAR. can i change it with 5GS?
    i am just worried that it will not damage the compressor in future?
    Thanks,
    Kamran.
    ireland
    1,450
    41
    Re: Urgent help:: Refrigerant oil york alternate
    What refrigerant are you running on? The York oils are specific to the chillers, hence the various types.
    alec
    Apr 2009
    Qatar
    44
    13
    R22 Gas & yes ita for YAEP chiller. its mentioned that YORK E oil should be used. but i cant find YORK E oil.
    ireland
    1,450
    41
    Have you had the oil tested, or has it leaked? It may be that it's ok.
    Alec
    Somerset
    70
    4,700
    47
    Kamran.
    4GS would be better or indeed any multi-purpose Mineral oil
    Apr 2009
    Qatar
    44
    13
    we are changing the oil for PM, as its not been chnaged from last 2 years. So GRIZZLY, shall i go for 4GS?
    i got following info from another forum.
    I test a lot of York C oil from chillers. It is a 300 SUS oil.
    I have the following information listed you may find useful:
    York A is a 300 SUS oil that is equivalent to Capella WF-68,
    York B is an additized blend if two non-refrigeration oils (never seen a sample from the field),
    York D is a 150 SUS oil that is equivalent to 3GS or Capella B,
    York E is a 500 SUS oil equivalent to 5GS,
    York F is a 150 SUS oil equivalenmt to 3GS.
    York G, H, J, O, P and S are all POE lubricants, typically made by CPI. The Frick oils normally match up with one of the York oils as well.
    Somerset
    70
    4,700
    47
    The above does not completely tally with the info I have, however.
    E is indeed Sus. 500.
    Is 5gs mineral or synthetic?
    I believe 4gs is mineral and therefore I assume cheaper?
    The ultimate choice is yours!
    Apr 2009
    Qatar
    44
    13
    but both will not damage the compressor operation in future and its efficiency? 5GS is mineral & i preffer it as its SUS is same & i think its better. but my concern is that i dont face any problem in operation.
  1. Alternate to ASHP
    By mikeh in forum New Technologies
    Last Post: 02-02-2010, 01:30 AM
  2. Alternate suppliers ?
    By eggs in forum Legal-Business-Marketing
    Last Post: 14-11-2004, 12:23 AM
Tags for this Thread