Thread: Hot gas solenoid valve
07-02-2011, 09:16 AM #1
Hi guys hope all is well
Just a quick one. I've been called to a close control Airedale chiller. The solenoid valve on the hot gas by pass is leaking at the base of the shaft where it enters the body of the valve. This is the third time this has happened in as many months. The valve used is just a standard run of the mill solenoid valve is this right ? or do you need a special type for use on the hot gas
07-02-2011, 09:54 AM #2
Re: Hot gas solenoid valve
hi kirky,
yes the HG valve is different cos there is adjustment on it , if you just opened a solinoid on the HG it would shoot streight through the system to the comp, and that would not last long,< it would overheat< hope that anawers your question , sedgy,
09-02-2011, 08:52 AM #3
Thanks mate that's most helpful.
09-02-2011, 04:48 PM #4
Sedgy do you know where I might purchase one of these adjustable HG solenoid valves
09-02-2011, 05:20 PM #5
hi kirky,
well if you get the number off the valve you could ask any wholesaler to order you one , if no number get the U number off the unit and ask airdale which HG valve they recomend < they will ask for the U number< if its brazed in strip down the valve and you could try some heat sink on the stem to get rid of any heat< or a wet rag < all the bnest with it kirky , sedgy,
09-02-2011, 06:52 PM #6
make sure the mag valve is rated for hot gas work. Danfoss have a range that covers this.
09-02-2011, 08:03 PM #7
Cheers guys i will speak to airedale tomorrow
18-02-2011, 03:56 PM #8
hey kirky,
come on now , tell us the outcome, did you get one?
Drier, Sight Glass, Solenoid valve , which order?
By Drew in forum CommercialReplies: 16Last Post: 16-06-2010, 05:43 PM -
Installation of Liquid Line Solenoid Valve
By aaronh in forum FundamentalsReplies: 14Last Post: 14-06-2010, 10:28 PM -
Pump down system, solenoid valve
By AleksanderNH in forum FundamentalsReplies: 6Last Post: 10-06-2010, 12:07 AM -
LEV does not open
By Yuri B. in forum Air ConditioningReplies: 7Last Post: 19-07-2009, 02:37 PM -
Liquid solenoid valve mystery
By mohamed khamis in forum ElectricalReplies: 20Last Post: 04-08-2008, 08:59 PM