Daikin PJ fault
Hi all.
Had one of our techs ring this afternoon with pj fault after changing outdoor boards.I know that its to do with setting the capacity of the existing unit but he claimed that the model he was working on wasnt on the list.Could not for the life of me find the install manual for pc boards in any of our manuals or data bases.Can anyone give me a link for it.Think it was a RX7 or RZ7
-
08-02-2011, 08:41 PM #2
Re: Daikin PJ fault
need rest of model no
-
08-02-2011, 10:39 PM #3
Re: Daikin PJ fault
RX7 or RZ7??
If the unit is a VRV system i.e. RXYQ- - You need to set the dip switches on the new PCB or if unit is a sky air i.e. RZQ you need to install the correct size capacity adapter plug into the new PCB.