    Daikin PJ fault



    Hi all.
    Had one of our techs ring this afternoon with pj fault after changing outdoor boards.I know that its to do with setting the capacity of the existing unit but he claimed that the model he was working on wasnt on the list.Could not for the life of me find the install manual for pc boards in any of our manuals or data bases.Can anyone give me a link for it.Think it was a RX7 or RZ7



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Daikin PJ fault

    need rest of model no

  3. #3
    Join Date
    Sep 2009
    Location
    Scotland
    Posts
    374
    Rep Power
    17

    Re: Daikin PJ fault

    RX7 or RZ7??

    If the unit is a VRV system i.e. RXYQ- - You need to set the dip switches on the new PCB or if unit is a sky air i.e. RZQ you need to install the correct size capacity adapter plug into the new PCB.

Similar Threads

  1. Daikin r407c 2 pipe vrv ja fault code any offers?
    By Contactor in forum Air Conditioning
    Replies: 11
    Last Post: 28-07-2009, 01:26 AM
  2. Daikin Split f3 Fault
    By moondawn in forum Air Conditioning
    Replies: 18
    Last Post: 01-06-2009, 07:09 PM
  3. Daikin Cassette Fault
    By symon22 in forum Air Conditioning
    Replies: 5
    Last Post: 23-05-2008, 06:19 PM
  4. UA Daikin Fault Code
    By jedi in forum Air Conditioning
    Replies: 2
    Last Post: 23-07-2007, 01:44 PM
  5. u4 fault on a Daikin inverter
    By phil17 in forum Air Conditioning
    Replies: 39
    Last Post: 05-02-2007, 02:41 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •