    hot gas defrost design



    Hi guys,

    just want to ask how to design a hot gas defrost for bare pipe in coldstorages

    regards,

    lynark



  2. #2
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: hot gas defrost design

    hi lynark, can you elaberate on the quote = for bare pipes in coldstorage?

  3. #3
    Join Date
    Jul 2005
    Location
    USA
    Age
    61
    Posts
    68
    Rep Power
    19

    Re: hot gas defrost design

    It will depend on the physical arrangement of the pipe array, the feed method, and the rest of the system.
    I am assuming that we are talking about antique refrigeration.

    Way back when, cold storage rooms had cork insulation (some used sawdust) the compressors were recips and instead of evaporator coils (with fans, tubes and fins) they ran bare steel pipe back and forth alond the walls and ceilings. The rooms depended upon natural air flow to move the warmer air across the piping to get the heat transfer. I saw a cut sheet from Frick advertising their Spiral Fin tubing which dated from the 1940's. If I recall correctly the pipe was 2" IPS.
    And if that is what you have, we would need a lot more information, you have to deal with the liquid refrigerant at the start of the defrost cycle, the oil in the pipe, the hot gas condensate, the melt water, what the heat load will do to the rest of the plant, your supply of hot gas and so on.

  4. #4
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: hot gas defrost design

    Hot gas defrost is best described as cool gas defrost by the time the actual gas gets to the evap coils, then the evap acts as a big oversized condenser before any ice disappears. Well that is my experience anyway. So you end up with an evap full of nice cold liquid.
    magoo

  5. #5
    Join Date
    Apr 2010
    Location
    philippines
    Posts
    36
    Rep Power
    0

    Re: hot gas defrost design

    Quote Originally Posted by McFranklin View Post
    It will depend on the physical arrangement of the pipe array, the feed method, and the rest of the system.
    I am assuming that we are talking about antique refrigeration.

    Way back when, cold storage rooms had cork insulation (some used sawdust) the compressors were recips and instead of evaporator coils (with fans, tubes and fins) they ran bare steel pipe back and forth alond the walls and ceilings. The rooms depended upon natural air flow to move the warmer air across the piping to get the heat transfer. I saw a cut sheet from Frick advertising their Spiral Fin tubing which dated from the 1940's. If I recall correctly the pipe was 2" IPS.
    And if that is what you have, we would need a lot more information, you have to deal with the liquid refrigerant at the start of the defrost cycle, the oil in the pipe, the hot gas condensate, the melt water, what the heat load will do to the rest of the plant, your supply of hot gas and so on.

    Yap thats the design of the coldstorage of our client... problem is there is "no" hot gas defrost in the system for the bare pipe so need to install one... but i gave limited knowledge in this type of system...

    regards,

    lynark

  6. #6
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: hot gas defrost design

    lynark,
    Even if you had hot gas defost how would you manage the melting ice?

    If you have a system of that vintage maybe you have a recip compressor with reversing
    valve manifold on it already
    ie 4 valve manifold that can be used for bypass start up, pumping out condensor into evaporator.These were used in days gone by for this reason.

  7. #7
    Join Date
    Jul 2005
    Location
    USA
    Age
    61
    Posts
    68
    Rep Power
    19

    Re: hot gas defrost design

    It might be possible to set up a hot gas system. Depending on how your customer's facility is set up there might be several methods.
    We are back at needing more details on the system.

  8. #8
    Join Date
    Apr 2010
    Location
    philippines
    Posts
    36
    Rep Power
    0

    Re: hot gas defrost design

    Dear Ranger1 and Franklin,

    Thanks again for the info. What are the details needed so we can start the hot gas design?

    Regards,

    Lynark

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. maytag fridge activation of new controller
    By jdrefrigeration in forum Domestic
    Replies: 5
    Last Post: 09-03-2010, 12:00 PM
  3. Toshiba RAV SM/SP1400 defrost problem
    By SteinarN in forum Heat Pumps
    Replies: 11
    Last Post: 20-02-2008, 04:25 PM
  4. No Power for Defrost Timer Motor
    By kln in forum Domestic
    Replies: 6
    Last Post: 21-01-2008, 08:22 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •