    Evaporater icing up.....



    Hello everyone, Long time lurker....first time poster...so take it easy....

    I understand TX valve superheating and the reason for it.

    My question is ....Would an incorrect superheat setting cause icing up of the evaporater...???

    Thanks for your help.....



  2. #2
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: Evaporater icing up.....

    Yes-not enough refrigerant getting to the evap could cause freezing

  3. #3
    Join Date
    Feb 2011
    Location
    United States
    Age
    56
    Posts
    5
    Rep Power
    0

    Re: Evaporater icing up.....

    I find this question hard to answer due to not enough information.

    Do you have defrost capability on this evaporator? Room Target Temp? Suction Pressure? How is this evap fed liquid?

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Evaporater icing up.....

    Quote Originally Posted by Scooter29 View Post
    Hello everyone, Long time lurker....first time poster...so take it easy....

    I understand TX valve superheating and the reason for it.

    My question is ....Would an incorrect superheat setting cause icing up of the evaporater...???

    Thanks for your help.....
    It would depend on the application.
    If you are talking A/C then I would doubt it. Assuming a fully charged system, an incorrect superheat setting (at design conditions) would either result in a flooded evap and liquid returning to the compressor with little or no superheat or evap starvation and a high superheat. As A/C is designed to evaporate around 5C there wouldn't be much sign of frosting. A gas shortage, or restriction would result in evap frosting.

    If you are talking refridge then the evaporating temp will be below freezing point anyway and the coil will frost. The superheat setting will determine either a fully frosted evap or a partially frosted evap.

Similar Threads

  1. Beko CDA660 Icing up
    By gekko in forum Domestic
    Replies: 8
    Last Post: 19-02-2011, 10:45 PM
  2. Outdoor coil icing up...
    By airflo in forum Heat Pumps
    Replies: 18
    Last Post: 28-10-2008, 07:12 PM
  3. Compressor suction icing up on cold room set up
    By Leviathan in forum Trouble Shooting
    Replies: 9
    Last Post: 02-06-2007, 05:08 AM
  4. Krack Evaporator Icing
    By Rob@goldcoast in forum Technical Discussions
    Replies: 11
    Last Post: 15-08-2006, 02:53 AM
  5. What causes the icing of the evaporator
    By donrtc in forum Technical Discussions
    Replies: 12
    Last Post: 19-08-2005, 12:35 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •