Re: Altherma flow temp issue
The 30 litres is to allow for a decent running period on the HP once it starts. You do not want to get into a stop/start cycle too frequently on a HP. If you go too small there will be no temp differential in your buffer and you're back to where you started and as you mentioned the compressor life will be shortened. Minimum buffer we would ever fit would be 300L, so even if the unit was a 7kw we would fit a 300L. From 10kw up you would calculate at 30L per kw. For your 16kw machine, fit a 500L buffer.
If you have water going to outside from your ufh you will need glycol. It all depends on the heatpump you run as to weather that is the case. We have done both but prefer where all heat is produced and remains indoors. If you use a HP which is producing heat externally and circulating it to the buffer, then I would consider using a coil on the HP side of the buffer, so only that small section of pipe (the circuit between HP and Buffer) need be filled with glycol. It'll save you money in terms of extra glycol and also the extra power that will be consumed by the ufh pumps when pumping glycol
Similar Threads
-
Controlling a compressor off suction line temp, or pressure
By desA in forum FundamentalsReplies: 13Last Post: 06-06-2010, 06:26 PM -
flow switch connection
By afeef in forum The Trail of TearsReplies: 18Last Post: 23-12-2009, 06:55 PM -
Residential A/C - Indoor air temp. off the chart?
By Bentus in forum Trouble ShootingReplies: 37Last Post: 09-07-2009, 03:10 PM -
Capillary Tube Characteristics
By Chef in forum FundamentalsReplies: 9Last Post: 10-03-2009, 01:03 PM -
Endless Freezer as Endless Cooler (10 door)
By herefishy in forum CommercialReplies: 95Last Post: 17-04-2002, 12:54 PM