    Hot water tank - condenser rupture - what will happen?



    We have a hot-water tank (called a geyser in SA), which has a safety relief valve set to 6 barg. Water inlet feed is at 4 barg.

    A pipe-coil condenser is placed inside the geyser. When the hot water is at 60'C, the condenser ruptures *suddenly* inside the geyser at 27 bar (alternatively at 42.6 bar).

    What will happen?


    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  2. #2
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Hot water tank - condenser rupture - what will happen?


  3. #3
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Hot water tank - condenser rupture - what will happen?

    LOL... it sure does.

    http://www.youtube.com/watch?v=0rXwcDkobUY&NR=1

    That is what I have been telling people. I've had responses that the gas will 'fizz' into the water and be absorbed. Not sure that nature will agree with that argument, though.
    Last edited by desA; 03-02-2011 at 06:07 PM.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  4. #4
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Hot water tank - condenser rupture - what will happen?

    Well... I'm not so sure. The refrigerant pressure would drop very quickly and the relief would pop.

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Hot water tank - condenser rupture - what will happen?

    The geyser safety valve should lift to release the pressure however it should, perhaps, be sized to accommodate the large increase in pressure over the steady increase expected.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Dec 2010
    Location
    Ireland
    Posts
    339
    Rep Power
    15

    Re: Hot water tank - condenser rupture - what will happen?

    I've seen an installation where a plate exchanger burst and vented into the ufh system and tank. No damage bar water in the refrigeration circuit. All displaced water vented through the relief valve. It really is no biggie

  7. #7
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: Hot water tank - condenser rupture - what will happen?

    Des, standard water heaters here are designed to double the rated pressure. This is the standard fudge factor. A 300l tank rated for 125 or 150 psi, as standard tanks here are, will need a much larger volume than the 20-30L of a refrig system hooked up to the coil in the tank to take 60psi to the burst pressure. The standard PRVs used on the tanks will let out 50kw instantly (well... after it drips for a while.

    I have had a solar system with 100L in volume and internal pressures of 25+ bar and temps of 200C (due to pump control failure) burst a flat plate HX and the 1500L tank PRV just started to drip (exp tank was toast though).

  8. #8
    lencerpetro's Avatar
    lencerpetro Guest

    Re: Hot water tank - condenser rupture - what will happen?

    It is the fact that the coolant pressure would drop very fast and the relief would pop. And it is also true the geyser safety valve must lift to relieve pressure, however, should perhaps be sized to accommodate the large increase in pressure at the steady increase expected.

  9. #9
    lencerpetro's Avatar
    lencerpetro Guest

    Re: Hot water tank - condenser rupture - what will happen?

    It is the fact that the coolant pressure would drop very fast and the relief would pop. And it is also true the geyser safety valve must lift to relieve pressure, however, should perhaps be sized to accommodate the large increase in pressure at the steady increase expected.


    Rainwater tanks

  10. #10
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Hot water tank - condenser rupture - what will happen?

    Thanks everyone for your comments. An interesting scenario that probably plays out different ways, depending on the RV sizing & selection.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  11. #11
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: Hot water tank - condenser rupture - what will happen?

    RV sizes are based on the maximum possible increase in energy (temp and/or pressure) expected with a failure of the heat source to limit itself. In Canada a standard 250L natural gas powered tank with a 10kw input (at 55% eff by the way) will have a relief valve setting of approx 75kw at 9 bar (approx) and ours have a temp failure at 95C usually.

    I know your tanks run at lower max pressure standards than ours do but given the energy available in the coil volume, can that safely be absorbed by the tank volume? Is there an expansion tank on the DHW system as we have to do more and more?

    Nice video on youtube but there is no PRV so it is irrevellant.

  12. #12
    Join Date
    Mar 2011
    Location
    Norway
    Posts
    29
    Rep Power
    0

    Re: Hot water tank - condenser rupture - what will happen?

    I guess that how fast the pressure will drop or build up, will depend of how much volum the tank and the tubes can expand. If there is some vapor, gas or air, some plase in the system, this will "take the first shock". If there is nothing that can take the first load by expanding, the one way or the other, it will be a question if the safety valve will be fast enough. I thinkt that there is only one way to know for sure, and that is to try it out. I guess that if the system were buildt with some a some kind of gass or air chamber that can be copressed, the system would be safer. (Because thsi would take the first shock out of it, if something should happen.)

Similar Threads

  1. Replies: 5
    Last Post: 19-05-2010, 02:54 PM
  2. Replies: 7
    Last Post: 07-02-2010, 09:33 AM
  3. water cooled condenser
    By philjd26 in forum Trouble Shooting
    Replies: 16
    Last Post: 18-11-2009, 02:46 PM
  4. Ice Bank Tank for Chilled Water
    By Samarjit Sen in forum Commercial
    Replies: 26
    Last Post: 31-10-2009, 09:18 AM
  5. Chilled water make up tank
    By camerond in forum Air Conditioning
    Replies: 1
    Last Post: 16-04-2009, 11:52 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •