Brazed Plate HX sizing help
hello I am trying to find information anywhere to the size of BPHE to use for condensor and evaporator for a ground source heat pump also the water flow and length of loop, I was going have a 5hp scroll to use and I was told that is comparable to 50,000 btu which would heat this house adequately any ideas would be appreciated or tell me to go to ref 101, which i did read
thanks ed,
-
03-02-2011, 08:20 PM #2
-
03-02-2011, 10:36 PM #3
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Brazed Plate HX sizing help
For R407C:
Evaporator capacity would be around 11 kW and condenser capacity would be around 15 kW.
What would be as heating element, fan-coils or underfloor heating?
What refrigerant is used?