    whats the max/min temp differential allowed



    before calling a mechanic thermostat deffective?

    i have one that set at 40ºF will keep the unit working till 32ºF and will start back at 70ºF

    I'm sure that is not normal so i opened the thermostat and everything seems to be ok.
    i checked it was placed, exactly in the same place and way before unmounting it and the conections are correct.

    it's a danfoss thermostat like one of these...





    sorry if you find this post irrelevant but i could use a hint as to if these can be recalibtated or disposed for new ones.

    thanks in advance



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: whats the max/min temp differential allowed

    2 to 3 K is normal termostat differential for air conditioning applications.
    For particular termostat you should found its technical literature, since differential depend on his usage field.

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: whats the max/min temp differential allowed

    Apart from changing to an electronic control, Eliwell, Dixell etc., is the sensing bulb in good contact to the fluid being sensed?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,853
    Rep Power
    46

    Re: whats the max/min temp differential allowed

    If it worked before and now doesn't, technicaly its broked and needs a new one.

  5. #5
    Join Date
    Jan 2009
    Location
    Earth
    Posts
    75
    Rep Power
    16

    Re: whats the max/min temp differential allowed

    ok so either the thermostat is broken (because it does not work as it used to) or I reinstalled the temperature bulb incorrectly.

    the thermostat as nike ponts out has a 3K differential and i placed the copper bullet at the air return side of the evaporator coil, where i found it in the first place, where should i place the temperature bulb to get the accurate measuring and prevent extended runtimes?

    thanks

  6. #6
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: whats the max/min temp differential allowed

    hi frostedflake, I seam to remember somthing about setting up the stat < file < it has to point downwards or the alchol or liquid inside the <file< migrates along the cappilary making the stat uncontrolable, also I remember there is a manual setting to give a max + min temp range,

  7. #7
    Join Date
    Jan 2009
    Location
    Earth
    Posts
    75
    Rep Power
    16

    Re: whats the max/min temp differential allowed

    thanks for the help

Similar Threads

  1. MP66 & Compressor Overheating
    By Intermez in forum Technical Discussions
    Replies: 111
    Last Post: 13-04-2010, 08:58 PM
  2. Replies: 5
    Last Post: 08-11-2009, 05:10 PM
  3. Temp. Rise at duct outlet
    By jwasir in forum Trouble Shooting
    Replies: 13
    Last Post: 10-05-2008, 04:22 PM
  4. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  5. cold room temp & the product temp
    By smpsmp45 in forum NH3
    Replies: 9
    Last Post: 21-09-2007, 11:46 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •