    weird Refrigeration



    hi all,

    i have an o6e recip running full load.

    77 amps fla
    running 52 amps

    suction 270 kpa
    Discharge 1800 kpa
    sst 8.5 C
    sct 49 C
    liquid pipe temp - 39 C
    Suction Pipe Temp - 21 C

    Running on 3 x TXV

    Air on evap - 26 C
    Air off Evsap 23 C
    condenser 18 k split

    Need to be seeing 10 k split over evap.
    Used to get it but another tech attended site, gas leak and now i cannot trim the charge correctly very frustrating any ideas?



  2. #2
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: weird Refrigeration

    Hi,
    I've no idea what an "o6e" is but i'll try and help.

    Firstly what refrigerant is it running on?

    With 10K subcooling and 12.5k superheat i would start looking at the TEVs for underfeeding.

    Are the filters clean and is the airflow correct in the evap?
    (This is assuming it isn't a chiller, If it start looking at your flow rates on your chilled water.)
    The difference between genius and stupidity is that genius has its limits.

    Marc

  3. #3
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: weird Refrigeration

    sst 8.5°C and suction temp 21°C for me mean clogged filter or coil, or air flow restriction.

  4. #4
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: weird Refrigeration

    Quote Originally Posted by marc5180 View Post
    Hi,
    I've no idea what an "o6e" is but i'll try and help.

    Firstly what refrigerant is it running on?

    With 10K subcooling and 12.5k superheat i would start looking at the TEVs for underfeeding.

    Are the filters clean and is the airflow correct in the evap?
    (This is assuming it isn't a chiller, If it start looking at your flow rates on your chilled water.)
    Hi Mark.
    An 06E is a carrier recip!
    The attached is a 07e but is very similar.
    Grizzly

  5. #5
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: weird Refrigeration

    Quote Originally Posted by Grizzly View Post
    Hi Mark.
    An 06E is a carrier recip!
    The attached is a 07e but is very similar.
    Grizzly
    Oh in that case i haven't a clue
    The difference between genius and stupidity is that genius has its limits.

    Marc

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: weird Refrigeration

    If you want a pretty picture of an 06E then...

    http://www.commercial.carrier.com/co...PRD211,00.html
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  7. #7
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: weird Refrigeration

    I would be looking for a plugged drier, liquid line kink or plugged TXV inlet strainer.

  8. #8
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: weird Refrigeration

    Also check for a dirty condenser.

  9. #9
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: weird Refrigeration

    Quote Originally Posted by Gary View Post
    Also check for a dirty condenser.
    Can i aks why check for a dirty condensor? If condensor become fouled suction superheat decreases doesn't it?
    The difference between genius and stupidity is that genius has its limits.

    Marc

  10. #10
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: weird Refrigeration

    Did the other tech put the correct refrigerant in it?

  11. #11
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: weird Refrigeration

    Quote Originally Posted by marc5180 View Post
    Can i aks why check for a dirty condensor? If condensor become fouled suction superheat decreases doesn't it?
    Separate problem. The condenser split seems high... especially with the evap severely underloaded. The primary problem would be liquid restriction.

    Over the years, I have found that multiple problems are the norm.
    Last edited by Gary; 04-02-2011 at 12:17 AM.

  12. #12
    Join Date
    May 2010
    Location
    Australia
    Age
    39
    Posts
    29
    Rep Power
    0

    Re: weird Refrigeration

    Could a restriction in the suction line cause this issue. There ia no restriction in the liquid line at all. Ahu filters are brand new Evap coil clean carried out a month ago. I like the blocked tx valve strainer idea. Will look into it.

  13. #13
    Join Date
    May 2010
    Location
    Australia
    Age
    39
    Posts
    29
    Rep Power
    0

    Re: weird Refrigeration

    And r22 gents

  14. #14
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: weird Refrigeration

    High discharge, low suction, if not drier look at failed TX valve. Liquid stacked in high side.

  15. #15
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    51
    Posts
    1,083
    Rep Power
    23

    Re: weird Refrigeration

    Hi Koopy
    This one sounds tricky with high discharge temp and high superheat with acceptable subcooling. A couple of things to check here - first touchy feely check for temp differences in the liquid and suction lines, like Gary (Mr Wisdom) said there could be more than one fault and monkey spanners is there a contaminant in the system (check history with previous tech). It would be prudent to search this forum to find link and download the O6E manual. From what you wrote it is a DX air cooled a/c system, what is the ambient and serial number?

  16. #16
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: weird Refrigeration

    High discharge temp means not much cold vapour coming down the suction line.
    High superheat means not much liquid passing through the TX valves into the evap.
    Subcooling good because that's where all the liquid is, in the condenser and liquid lines.

    Like gary said, liquid line problem, drier, strainers or TX valves themselves.

    edit:
    Quote Originally Posted by Koopy View Post
    Could a restriction in the suction line cause this issue. There ia no restriction in the liquid line at all. Ahu filters are brand new Evap coil clean carried out a month ago. I like the blocked tx valve strainer idea. Will look into it.
    Could, but you are going to have some serious frosting at the restriction if it's in the suction line. Also where are you measuring your suction pressure? If at the compressor, then suction line problem a possiblity, but if you measure low pressure at the evap itself, then that shows the problem before the evap in the liquid line as said.
    Last edited by paul_h; 04-02-2011 at 12:35 PM.

  17. #17
    Join Date
    Feb 2011
    Location
    Australia
    Age
    38
    Posts
    3
    Rep Power
    0

    Re: weird Refrigeration

    Carried out further repairs on same unit, changed driers (partially blocked), pressure and leak tested properly, evacuated system to below 500 microns, then charged system and is now running fine.

    I came to the conclusion that the system was full of non-condensable's due to low or no vacuum done on original job.

    Amazing what you can achieve when you take the time to do the job properly.