    ROTEX HPSU / DAIKIN ALTHERMA 11kW "ERROR U2"



    Hello Experts!

    Having problems since NOV-2010 with my ROTEX HPSU units. Outer unit's fan starting up 30 secs. and then shutting down. Display on inner unit showing Error-Code U2.
    System is from now on running only on immersion heating element.

    After restart or reset of fuse same procedure.

    ROTEX told, that compressor in outer unit can not started, so they replaced board in internal unit but are clueless now, as error is still shown...

    Any ideas??



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: ROTEX HPSU / DAIKIN ALTHERMA 11kW "ERROR U2"

    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: ROTEX HPSU / DAIKIN ALTHERMA 11kW "ERROR U2"

    altherma fault codes differ from standard daikin fault codes =U2 Abnormal Inverter Circuit Power Supply Check power supply, check bridge rectifier, check fan motor, is inverter input voltage approx >280Vdc

  4. #4
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: ROTEX HPSU / DAIKIN ALTHERMA 11kW "ERROR U2"

    It is important that the capacitor is connected correctly on the DC side of the inverter circuit, if this is incorrect the wave form will be incorrect and this error can occur with a new printed circuit board installed. the colours are grey and orange. Make sure that the reactor is connected with a good connection these are 2 x white cables.

    If there is still a U2 fault then the problem can be that there is low voltage to the unit, the outdoor fan motors or compressor can also cause this, start with metering the compressor resistance and input voltage to the unit on start up.

Similar Threads

  1. Daikin Altherma
    By frank in forum Domestic
    Replies: 86
    Last Post: 14-02-2011, 10:28 PM
  2. Replies: 9
    Last Post: 02-02-2011, 09:39 AM
  3. How are the Daikin Altherma units?
    By LucMan in forum Air Conditioning
    Replies: 11
    Last Post: 15-07-2010, 11:08 PM
  4. Daikin Altherma Rotex HPSU + Sanicube Hydrocube
    By hsmith in forum Heat Pumps
    Replies: 2
    Last Post: 15-07-2010, 10:44 PM
  5. Altherma from Daikin
    By Scott Samson in forum New Technologies
    Replies: 25
    Last Post: 20-02-2009, 11:03 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •