    Effects of oversizing condenser



    Application: Walk-in Coolers to maintain 35F. Units will be used to train refrigeration students.

    Maximum room size: 71" x 71" x 84"
    Compressor: MUST be semi-hermatic (since it is for training)
    ---------------------------------------------------------
    The smallest semi-hermatic compressor being manufactured by Copeland and Bitzer is 1HP. This is too large for the room size and the compressor is expected to short cycle.

    Is there a way around this? The constants here are the room size, semi-hermatic and to maintain temperature.

    If we oversize the compressor for the room, what are the drawbacks? Remember that the unit is to be used for training purposes.

    Thanks.
    Yasir



  2. #2
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Effects of oversizing condenser

    That size enclosure is an oversized coffin, the 1 HP compressor will cycle on low load real quick.
    See if a can manufacturer will supply an accessable hermetic compressor.
    They did years ago for small recovery units. They had a vee band around the normally welded joint on compressor can

  3. #3
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: Effects of oversizing condenser

    I don't understand: the thread is "Effects of oversizing condenser" but post is about oversizing compressor.
    Nevertheless, if you use oversizing compressor, than evaporating temperature would decrease and if compressor is oversizing enough than it will stoped by low pressure control.
    In your case, it depends what evaporator and condenser you use and what evaporating temperature you need.
    In some cases you may use:
    1) evaporating pressure regulator such as KVP (Danfoss)
    2) crankcase pressure regulator such as KVL (Danfoss).
    It both cases there are energy loss...
    As regurds me, I prefer install hermetic compressor essential capacity
    In some places will have to think ...

  4. #4
    Join Date
    Nov 2004
    Location
    China
    Posts
    176
    Rep Power
    20

    Re: Effects of oversizing condenser

    It's for training, don't add a bunch of control valves to confuse the students. Better to add a fan & grill on opposite walls and add warm room air to the refrigerated room to balance the load. Use a variable speed fan and you can vary the load to teach the effect of oversize and undersize systems, reduced loads etc.

Similar Threads

  1. oversizing condenser fan motors?
    By delta T in forum Electrical
    Replies: 3
    Last Post: 14-07-2010, 04:58 AM
  2. oversizing condenser fan motors?
    By delta T in forum Chit Chat & Service Stories
    Replies: 5
    Last Post: 13-07-2010, 02:20 PM
  3. Replies: 2
    Last Post: 08-06-2010, 11:12 PM
  4. How to measure COP (evaporative condenser)
    By Juho in forum Technical Discussions
    Replies: 5
    Last Post: 04-06-2010, 07:08 PM
  5. Evaporative Condenser system COP
    By Juho in forum Commercial
    Replies: 0
    Last Post: 03-06-2010, 09:23 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •