    undercharged?



    Newbie!!

    Got a low discharge temp on compressor 48c icing back on suction.......undercharged?



  2. #2
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: undercharged?

    hi welder , have you got clean filters ? is the evap fan running < full revs<? sedgy ,

  3. #3
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: undercharged?

    Quote Originally Posted by Welder View Post
    Newbie!!

    Got a low discharge temp on compressor 48c icing back on suction.......undercharged?
    A lot more information is needed to know if it is undercharged such as;

    What is the superheat?
    What is the subcooling? ( if applicable)
    What type of expansion device? Fixed or tev?
    Air on/off indoor unit
    Air off outdoor unit etc etc
    The difference between genius and stupidity is that genius has its limits.

    Marc

  4. #4
    Join Date
    Dec 2010
    Location
    devon
    Age
    53
    Posts
    837
    Rep Power
    24

    Re: undercharged?

    if iceing suction heavily its overcharged or if it has a tev its bypassing is the coil iceing when the suction pipe is? more ifo required ie temps tev or cap type of machine superheat as above really

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: undercharged?

    Welder, as Marc says, you really must start giving a few more facts if you want a decent answer.

    It's a bit like me saying that I have a 36" waist, what colour are my eyes and why?

    One single reading and a quick look do not a diagnosis make.

    You've got 48°, is that air temperature, the temperature of your gas torch cooling down or your coffee from Costa's?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Dec 2007
    Location
    lebanon
    Posts
    130
    Rep Power
    17

    Re: undercharged?

    hi
    if you meant an air condition system its under charge but if it is a refrigeration system more info more help

Similar Threads

  1. Undercharged vrv system symptoms?!??
    By weidit in forum Air Conditioning
    Replies: 18
    Last Post: 08-07-2010, 11:05 AM
  2. Replies: 33
    Last Post: 21-02-2010, 01:29 PM
  3. system recharge
    By Bachuss in forum Fundamentals
    Replies: 53
    Last Post: 30-07-2009, 09:28 AM
  4. Undercharged and Overcharged Symptoms
    By oscar-uk in forum Training
    Replies: 5
    Last Post: 17-04-2009, 02:10 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •