Results 1 to 6 of 6
Thread: undercharged?
-
30-01-2011, 11:32 AM #1
undercharged?
Newbie!!
Got a low discharge temp on compressor 48c icing back on suction.......undercharged?
-
30-01-2011, 12:02 PM #2
Re: undercharged?
hi welder , have you got clean filters ? is the evap fan running < full revs<? sedgy ,
-
30-01-2011, 02:08 PM #3
Re: undercharged?
The difference between genius and stupidity is that genius has its limits.
Marc
-
30-01-2011, 03:42 PM #4
Re: undercharged?
if iceing suction heavily its overcharged or if it has a tev its bypassing is the coil iceing when the suction pipe is? more ifo required ie temps tev or cap type of machine superheat as above really
-
30-01-2011, 07:32 PM #5
Re: undercharged?
Welder, as Marc says, you really must start giving a few more facts if you want a decent answer.
It's a bit like me saying that I have a 36" waist, what colour are my eyes and why?
One single reading and a quick look do not a diagnosis make.
You've got 48°, is that air temperature, the temperature of your gas torch cooling down or your coffee from Costa's?Brian - Newton Abbot, Devon, UK
Retired March 2015
-
30-01-2011, 07:32 PM #6
Re: undercharged?
hi
if you meant an air condition system its under charge but if it is a refrigeration system more info more help
Similar Threads
-
Undercharged vrv system symptoms?!??
By weidit in forum Air ConditioningReplies: 18Last Post: 08-07-2010, 11:05 AM -
Symptoms of outdoor unit being undercharged in heat mode?
By back2space in forum Heat PumpsReplies: 33Last Post: 21-02-2010, 01:29 PM -
system recharge
By Bachuss in forum FundamentalsReplies: 53Last Post: 30-07-2009, 09:28 AM -
Undercharged and Overcharged Symptoms
By oscar-uk in forum TrainingReplies: 5Last Post: 17-04-2009, 02:10 PM