    Hi all,
    I've just intalled a city multi at a store, one outdoor,4 cassetse,and one controller.
    the question i have is there any way of locking the temp set point on the controller to stop the staff at the store from messing about with it
    Any help much appreciated
    mant thanks.



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: City Multi

    on a par21 The following settings can be made.
    no1 :All buttons except for the [ON/OFF] button are locked.
    no2 :All buttons are locked.
    OFF (default) :No buttons are locked.
    * To activate this operation lock function on the normal screen, hold down the
    ON/OFF button for two seconds while

    holding down the
    FILTER ( ) button

  3. #3
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,876
    Rep Power
    28

    Re: City Multi

    Or if you have a Par 27 to lock all the buttons other then the on/off button,
    Press the [on/off] button for 2 seconds whilst holding down the [FILTER] button.

    Alternatively you could also set a temperature range limit on the controller.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: City Multi

    temperature limit settings are
    (1) While pressing the
    MODE button, press the ON/OFF button for two seconds to activate the remote controller’s
    function selection mode.
    (2) Press the
    MODE button to select FUNCTION
    SELECTION
    on the screen (at ).
    [Display ]
    (3) Press the
    MENU button to select LIMIT TEMP
    FUNCTION
    on the screen (at ).
    * If a setting change was made previously, the mode that was set (one of the modes shown in step (4)) will be displayed.
    (4) Press the
    ON/OFF button to select the mode for which temperature range limit setting is to be made.
    [Display ]

    * No operation modes will be displayed if auto mode has been set to OFF
    Press the button to select lower limit or upper limit.
    Lower limit blinks. Upper limit blinks.
    [Display ]
    (6) Press the [TEMP] buttons ( and ) to set the desired temperature setting range.
    [Setting example for lower limit]
    (7) While pressing the
    MODE button, press the ON/OFF button for two seconds to return to normal mode. Setting is
    now complete.
    * If you press the
    ON/OFF button before the MODE button, the settings you have made will be cancelled.
    * If an attempt is made to set a temperature outside the range when the temperature range limit function is in use, “LIMIT

    TEMP FUNCTION” will blink.

  5. #5
    Join Date
    Dec 2009
    Location
    wales
    Posts
    5
    Rep Power
    0

    Re: City Multi

    thanks everyone for the replies, will give it a go on monday.
    cheers

Similar Threads

  1. Multi City
    By spikybm in forum Trouble Shooting
    Replies: 4
    Last Post: 03-09-2010, 08:53 PM
  2. RS44 R424a in City Multi
    By Collie in forum Refrigerants
    Replies: 2
    Last Post: 22-07-2010, 05:56 PM
  3. City Multi Undersized
    By MOVHVAC in forum Air Conditioning
    Replies: 3
    Last Post: 20-07-2010, 06:46 PM
  4. City Multi Faults
    By Collie in forum Air Conditioning
    Replies: 2
    Last Post: 22-06-2010, 06:13 PM
  5. Need input on City Multi
    By TDfromNY in forum Air Conditioning
    Replies: 4
    Last Post: 09-06-2006, 03:31 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •