    Faulty meat multi-deck cabinet



    Hello fellow engineers,

    I was hoping someone might be able to help me on a refrigeration fault.

    I've got a problem multi-deck which contains two evaps which are piped up to one condensing unit. The right hand side gets down to setpoint of 0 degrees, however the left hand side runs between 5-8 degrees. If I turn the right hand side coil off, the left hand coil will get down to setpoint which again is 0 degrees.

    This HT case is on R404A, contains mercury controllers and network modules. It runs at 1.8 bar L/P either one coil is in demand or both, however pressure will drop down to 0.5 bar for a while then go back to 1.8 bar . The H/P runs at 10 bar which seems normal and the sight glass is clear.

    This case was only installed last August and has had several engineers investigate this fault already. I would be grateful if anyone could suggest any ideas on what could be causing the fault.

    Kind regards,

    Pie Man



  2. #2
    Join Date
    Feb 2009
    Location
    Australia
    Posts
    272
    Rep Power
    16

    Re: Faulty meat multi-deck cabinet

    pie man,
    sounds like an old austral twin coil case,,,i would look at the superheat on the tx valve.if it's an alco balanced port tx,,,replace both of them with danfoss.if the valves are alco they are your problem.
    Lawrie
    Remember we are here for a good time, not a long time.
    Trust me i'm a Fridgy.

  3. #3
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: Faulty meat multi-deck cabinet

    LP set too low?

    Could be a few things really.

    Chillin
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  4. #4
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: Faulty meat multi-deck cabinet

    Pie man, so.. either left or right will reach temp when cooling for both is not called for. So i would say that there is either a problem with the size of liquid line, or problem with the distribution. Maybe liquid feeds one tx then with a tee, the second tx gets supply. In other words, if both valves are feeding, the one with the shortest run will starve the second. If liquid line is wrong size, then same conditions will apply. Sight glass will show clear as it is not showing condition at the tx valve.. Mike
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  5. #5
    Join Date
    Feb 2009
    Location
    USA
    Age
    54
    Posts
    143
    Rep Power
    16

    Thumbs up Re: Faulty meat multi-deck cabinet

    I agree with Mikeref.

  6. #6
    Join Date
    Aug 2008
    Location
    Auckland
    Age
    55
    Posts
    259
    Rep Power
    21

    Re: Faulty meat multi-deck cabinet

    Put a sightglass in the liquid line directly prior to the TX, one of those male/female sightglasses can be fixed directly to the TX. Then you'll know fairly quickly if one of the valves is being starved of liquid when both are calling for cooling.

  7. #7
    Join Date
    May 2008
    Location
    ENGLAND
    Posts
    61
    Rep Power
    16

    Re: Faulty meat multi-deck cabinet

    Thanks guys for your comments. Got a call from an engineer today, the cabinet fault has bounced in again. He's been there most of the day and found out there original problem was do with the solenoid valves which were not wired correctly and the installers went back to 'fix' the problem. He's sure even though both coils require cooling only one solenoid will open hence starving the other. He's gonna contact our manager and try to get whoever installed back to site.

    Will keep you guys up to date and hopefully get some answers. I'm going back on site tuesday.

    Thanks for your replies,

    Pie Man

  8. #8
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: Faulty meat multi-deck cabinet

    O.K. Not even my usb plasma light could see that one on the horizon. Thanks for getting back to us.. mike.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  9. #9
    Join Date
    May 2008
    Location
    ENGLAND
    Posts
    61
    Rep Power
    16

    Re: Faulty meat multi-deck cabinet

    Hello guys,

    Went back to site today with another engineer, we found the left hand coil was iced up on the expansion valve after the orifice. Checked the orifice, was blocked hence causing the pressure to go into a vacuum. Replaced that but still no affect. Therefore concluded the soldered exp v/v was goosed. Replaced and now getting down to temp fine.

    Pie Man

Similar Threads

  1. Blast freezing of meat
    By b.tikekar18 in forum Technical Discussions
    Replies: 10
    Last Post: 26-01-2011, 12:10 PM
  2. Multi deck island deli case
    By joe magee in forum Supermarket Refrigeration
    Replies: 7
    Last Post: 08-11-2010, 03:42 PM
  3. Multi temp cabinet
    By hundred in forum Technical Discussions
    Replies: 0
    Last Post: 18-12-2009, 10:01 AM
  4. Multi deck maintenance
    By Andy AC in forum Commercial
    Replies: 5
    Last Post: 29-07-2009, 01:44 AM
  5. Where from can I get compresssor to Multi deck chiller?
    By Ceez in forum Supermarket Refrigeration
    Replies: 3
    Last Post: 16-06-2007, 06:08 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •