    I can have that problem too if subcooled ammonia?'m in a very hot part of mexico and now I have low temperatures ammonia is 10 ° c





  2. #2
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: low temperature amonia liquid

    Hi, serviceman

    Quote Originally Posted by serviceman View Post
    I can have that problem too if subcooled ammonia?'m in a very hot part of mexico and now I have low temperatures ammonia is 10 ° c

    Why do you think you should have a problem if your refrigerant is subcooled?

    Can you describe your plant and doubts little more, please?

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  3. #3
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: low temperature amonia liquid

    ????What is the question... If nothing else, post in Spanish..

    Ken

  4. #4
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    53
    Posts
    282
    Rep Power
    15

    Re: low temperature amonia liquid

    the system is a chiller with ammonia, I found fluid in the suction tank, we have been measuring the temperature of liquid ammonia and has been very low, the day yesterday was 5 ° C the liquid ammonia storage tank before entering the suction and 4 ° c.estas out temperatures could cause a return of liquid to the compressor?

  5. #5
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: low temperature amonia liquid

    what kind of system are you using?
    DX , Flood system , evaporate system?

    in Dx system's check expansion valve ,
    in flooded system check level controlling system .
    In evaporate system check throttle valve (how much it is open) and also check solenoid valve are closing well during off times?

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. NVQ 3 online test
    By Burrah Boy in forum Training
    Replies: 7
    Last Post: 28-10-2009, 08:35 PM
  3. Over charged system... what symptoms?
    By Clk320_Greg in forum Trouble Shooting
    Replies: 2
    Last Post: 19-10-2009, 06:25 PM
  4. TK basic micro-p features and functions
    By REEFER-TEK in forum Transport
    Replies: 0
    Last Post: 05-12-2007, 06:25 PM
  5. Replies: 9
    Last Post: 15-10-2007, 09:57 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •