    hi guys, doing a comp change next week on a VRV, inverter driven comp is down to earth, I haven't done an oil test but I am worried about oil in system and the other comp, if the oil has circulated around system. DOL comp is a scroll

    I plan on either using acid away, anyone used this before? isit good? or pulling oil out of DOL comp (hermetic)

    to pull the oil out I was thinking I might try and use an empty reclaim bottle (with Liquid and vapour connections) and use vac pump to pull it out (hose down suction pipe of comp, save completely sweating it out), if i do this is it consider ok to weigh the oil out rather than a ml measure? for replacement amount?

    http://www.nucalgon.com/assets/prodlit/3-78.pdf this would do the job but seems a waste of £ if my method is safe?

    how would you guys go about it?

    thanks
    Last edited by SkyWalker; 27-01-2011 at 07:39 PM.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Oil Change due to comp burnout

    Which make is the unit?

    Seem to remember that Daikin did an oil kit for compressor changes which included the drain pan, new oil and bits. (Could be wrong though)
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Oil Change due to comp burnout

    Quote Originally Posted by SkyWalker View Post
    or pulling oil out of DOL comp (hermetic)

    to pull the oil out I was thinking I might try and use an empty reclaim bottle (with Liquid and vapour connections) and use vac pump to pull it out (hose down suction pipe of comp, save completely sweating it out

    how would you guys go about it?
    I've never done or seen anyone put a hose down the suction port of a compressor and suck the oil out?

    Can it be done?

    Personally, I would take the compressor out and pour the oil out of the suction port.
    Still not 100% guaranteed, but the remaining oil should then dilute with the new oil, which should be monitored and changed as necessary

  4. #4
    Join Date
    Mar 2006
    Location
    belfast
    Posts
    239
    Rep Power
    19

    Re: Oil Change due to comp burnout

    drill the shell and weld in a schyder

  5. #5
    Join Date
    Nov 2006
    Location
    At home
    Posts
    181
    Rep Power
    18

    Re: Oil Change due to comp burnout

    hi guys, Brian not to sure on the model cant remember sorry, Frank I was trying to avoid having to completely remove the comp just to get oil out

    bigcheese, thanks for your post but i don't like the sound of that, and the fact i don't own a welder doesn't help!

    what about acid away? anyone used it? I went to buy an oil test kit from the wholesalers last year and they said many people just buy "acid away" and don't test, they buy a test kit as there similar priced, acid or no acid with "acid away" the oil will be neutralised???

    and weighing oil instead of measuring in a container? if I use reclaim bottle i want to leave it there until a later date you see and i wouldn't be able to see how much was there, weighing would be my only option unless i drain it out.
    Last edited by SkyWalker; 27-01-2011 at 08:19 PM.

  6. #6
    Join Date
    Mar 2006
    Location
    belfast
    Posts
    239
    Rep Power
    19

    Re: Oil Change due to comp burnout

    by weld i meant silver solder,

    try it on an old comp its not too bad

    i wouldnt do it on a good system unless i needed too ie real bad oil problems or retrofit etc

  7. #7
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Oil Change due to comp burnout

    Quote Originally Posted by frank View Post
    I've never done or seen anyone put a hose down the suction port of a compressor and suck the oil out?

    Can it be done?

    Personally, I would take the compressor out and pour the oil out of the suction port.
    Still not 100% guaranteed, but the remaining oil should then dilute with the new oil, which should be monitored and changed as necessary
    Yes you can but it depends on the type of compressor, bigger the better. You need the oil to be nice and hot and to have some thin and very flexible tube. I use model car silicon fuel hose. Measure how far it is from the suction port to the bottom of the comp and use that as a guide as to how much to feed in. It takes ages as the hole in the fuel tube isn't much bigger than a pressure couple.
    I use an old disposable cylinder i have brazed a 1/4" tap on, vac on the original tap. You can never be sure how much oil is left in unless the comp has a sightglass.
    A little ofn will push the oil back out again so you can measure how much you have removed.

    I think i would be tempted to remove the comp and tip the oil out, but it would depend on the unit, comp, etc.

    I have not tried the acid away stuff.

    Jon
    Last edited by monkey spanners; 27-01-2011 at 09:20 PM. Reason: because i can

  8. #8
    Join Date
    Nov 2006
    Location
    At home
    Posts
    181
    Rep Power
    18

    Re: Oil Change due to comp burnout

    ok monkey thank you, i might just remove it like you say, but hey its nice to try and make life a little easier, i was thinking of using a refer line but like you say this will be too rigid.

  9. #9
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Oil Change due to comp burnout

    I'm not a fan of acid away, i don't buy into it ! Fair enough you may neutralise the "acid" in the system . But that's no guarantee you're dealing with possible washout containments due to a burnout such as shelac debris and the like.
    A lot of original manufacturers offer similar stuff ! best check with them ,no point spending big bucks on a compressor and using acid away only to find the OM doesn't agreee , and your warranty and the clients is void .
    Cheers
    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  10. #10
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Oil Change due to comp burnout

    This is the sort of tube i have used for tricky comps.

    http://cgi.ebay.co.uk/FUEL-TUBE-sili...item230da7edaa

    And on this vid there is some random monkey showing the oil sucky thing in action, start viewing from 1 minute...

    http://www.youtube.com/watch?v=d5N9cqk-We0

    You might not want to cut your comp open though

    Also you can get an idea of the things the tube can get caught on as you feed it in, this is why it needs to be super flexible.

  11. #11
    Join Date
    Apr 2008
    Location
    UK
    Posts
    215
    Rep Power
    17

    Re: Oil Change due to comp burnout

    I have used acid away before, but after oil testing a year later the acidity has returned.
    There's also a max ratio of acid-away to oil that can be used so if you re-test at a later date & the acidity has returned, you may have to carry out an oil change any way..
    Depends how bad the burn out is realy. It's an option & although easy, it's but by no means the best long term option.
    Oil & filter/drier changes are the way to go in my opinion & preferably a new gas charge.
    Also not forgetting to identify why the burn-out occured in the first place..

    Last edited by Gingerair; 27-01-2011 at 11:21 PM.

  12. #12
    Join Date
    Dec 2009
    Location
    Spain
    Age
    45
    Posts
    229
    Rep Power
    15

    Re: Oil Change due to comp burnout

    Hi,

    Acidaway neutralises acids, but, how much acid do you have in the circuits? hence, how much acidaway do you need?
    Besides, acids are spread all trhough the installation, and you won't be sure you have eliminate all acid.

    At the end, you have to recover all the stuff you have put, which is a diffilcult task. But, besides, there might still be some acid around,... some acidaway, and still part of the substance obtained by the reaction between acidaway and acids...

    All these substances will remain in the "syphons" of the circuits, and you won't get them out just by blowing with N2.

    If you then put new oil, it would get contaminated as well with the rest of acid remaining there, and your problem will remain.

    Regards,

    Nando.
    Last edited by Fri3Oil System; 28-01-2011 at 11:27 AM. Reason: Treribel spellnig, soryr gusy XD

  13. #13
    Join Date
    Apr 2008
    Location
    UK
    Posts
    215
    Rep Power
    17

    Re: Oil Change due to comp burnout

    Thanks Nando, good to see you back..


  14. #14
    Join Date
    Dec 2009
    Location
    Spain
    Age
    45
    Posts
    229
    Rep Power
    15

    Re: Oil Change due to comp burnout

    Quote Originally Posted by Gingerair View Post
    Thanks Nando, good to see you back..

    Cheers Gingerair,

    just been watching from the shadow, I never was out.

    Regards,

    Nando.

  15. #15
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: Oil Change due to comp burnout

    Don't modern AC scrolls have the shell at discharge pressure instead of the suction?

    If you were to poke a tube down the suction pipe it would go into the scroll part not the bottom of the pot. Might need to check how your compressor is constructed first.

    Andy.
    Health and safety first..........unless I'm in a hurry.

  16. #16
    Join Date
    Jul 2009
    Location
    Illinois
    Posts
    187
    Rep Power
    15

    Re: Oil Change due to comp burnout

    I am a little confused by this thread, I often have to read and re-read posts as I am American and frequently do not fully understand the european lingo, however am I understanding that you are changing out a compressor and want to know about acid away? If you are changing out the compressor you shouldnt need to suck or push the oil out of it, remove it install the new compressor and use manufacturer oil quantity recomendation. If I am misunderstanding this and you need to remove oil from a compressor copeland makes just what you are looking for it is a dip tube you cut to length and it comes with a valve it can be left in the compressor for future oil changes. I would not use the acid away I would install a removable core suction drier and change it as well as the oil as often as is necessary to eliminate any acid.

  17. #17
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: Oil Change due to comp burnout

    Word Up Em,

    The system has 2 compressors. One is being replaced but the question regards the oil in the other compressor.

    Yer ol' mucker,
    Andy.
    Health and safety first..........unless I'm in a hurry.

  18. #18
    Join Date
    Jul 2009
    Location
    Illinois
    Posts
    187
    Rep Power
    15

    Re: Oil Change due to comp burnout

    Hey thank you for explaination Tayters, I still would not!!! use acid away, I have had good sucess with the dip tube and suggest you try it, if you have acid it is imparitive that you properly clean the system, add a drier as I suggested and multiple oil changes, it can be a lot of work but you wont regret it, you will have a happy customer and will not be doing any warranty work on that unit. By the way do you know what caused the failure? I highly recommend that you investigate the system throughly when you have replaced the compressor. I am currently following up on a unit that other technicians have replaced the compressor in several times in the last 3-4 years. it seems that they just replaced the component with out ever knowing why.

  19. #19
    Join Date
    Dec 2009
    Location
    Spain
    Age
    45
    Posts
    229
    Rep Power
    15

    Re: Oil Change due to comp burnout

    Quote Originally Posted by Emmett View Post
    Hey thank you for explaination Tayters, I still would not!!! use acid away, I have had good sucess with the dip tube and suggest you try it, if you have acid it is imparitive that you properly clean the system, add a drier as I suggested and multiple oil changes, it can be a lot of work but you wont regret it, you will have a happy customer and will not be doing any warranty work on that unit. By the way do you know what caused the failure? I highly recommend that you investigate the system throughly when you have replaced the compressor. I am currently following up on a unit that other technicians have replaced the compressor in several times in the last 3-4 years. it seems that they just replaced the component with out ever knowing why.
    Hi Emmet,
    still using acid away, and putting filters won't remove acids 100%. Multiple oil changes means a lot of labour as you said, and you won't be sure 100% taht you did remove the acids 100%.

    You can get rid of it in one operation. In the USA you might be able to get a machine from Van Steenburgh, though I never saw it working, it uses more or less the same principles of our machine, so it should do a similar job, without any consumables such as acid away or lots of oil to be changed. Don't forget how "funny" is afterwards to get rid of the acid away when you finish that job.

    Regards,

    Nando.

Similar Threads

  1. Compressor Change Daikin RZQ 100 B
    By MrThin in forum Air Conditioning
    Replies: 6
    Last Post: 13-05-2011, 10:59 AM
  2. Basics or is it?
    By Fett in forum Fundamentals
    Replies: 17
    Last Post: 10-09-2009, 01:45 AM
  3. Third comp change in three years, why?
    By expat in forum Commercial
    Replies: 44
    Last Post: 16-10-2008, 03:48 PM
  4. propane comp.
    By jehad_bahrain in forum Refrigerants
    Replies: 3
    Last Post: 17-05-2008, 12:26 PM
  5. comp oil
    By headgasket in forum Technical Discussions
    Replies: 2
    Last Post: 14-10-2007, 07:34 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •