    Think i know the answer to this one but didnt know whether any one had any ideas?

    Daikin single split losing pressure located leak on outdoor unit liquid side valve.

    valve core (Shreadar)(Spelling!) had a been bent and threfore pin wasent sitting straight.

    Pumped system down and attempted to remove existing valve core but the thread snapped all the way round thus not letting me remove the valve core


    Any ideas or is it just a new valve jobby?

    TA.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Any Ideas??

    A Daikin will probably have a high side access port inside the casing so just refit the port cover, ensuring a good seal, and label it as a damaged Schraeder - do not use.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Mar 2006
    Location
    belfast
    Posts
    239
    Rep Power
    19

    Re: Any Ideas??

    flare a new schyder on over the top of the damaged one, great trick pulled me out loadsa times

  4. #4
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: Any Ideas??

    hi av,
    would have used a shrader extraction tool to change it with the gas in the system,
    regards sedgy

  5. #5
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Any Ideas??

    Quote Originally Posted by thebigcheese View Post
    flare a new schyder on over the top of the damaged one, great trick pulled me out loadsa times
    The best way! Do it all the time whenever a schreader valve leaks.

Similar Threads

  1. Ideas Needed For Cooling My Glass Blowing Studio
    By JontheFisherman in forum Air Conditioning
    Replies: 17
    Last Post: 28-04-2011, 01:04 AM
  2. Daikin split problem (any ideas)
    By airconjohn in forum Air Conditioning
    Replies: 14
    Last Post: 17-02-2008, 08:40 PM
  3. need 12 volt car AC ideas
    By ayaz in forum Transport
    Replies: 5
    Last Post: 24-07-2007, 03:39 AM
  4. Need ideas !!!
    By zvikard in forum Technical Discussions
    Replies: 5
    Last Post: 17-08-2006, 08:34 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •