    compressor discharge temps



    Any advice on R22,R407c and R410A expected compressor discharge temps?



  2. #2
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: compressor discharge temps

    Welder,
    It all depends on the pressure ratio, discharge/suction pressure and superheat temperature...and also of the compressor type and brand.

    it could be between 50ºC...120ºC but also it could be out of this range...like I said all depend of the operating conditions.
    To make progress is never good enough, I want to do better and better and better

  3. #3
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: compressor discharge temps

    If I not mistaken, besides compressor type it also depends on type of oil...
    In some places will have to think ...

  4. #4
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: compressor discharge temps

    yes, also agree. However I think that have a 2nd order importance.
    To make progress is never good enough, I want to do better and better and better

  5. #5
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    52
    Posts
    1,083
    Rep Power
    23

    Re: compressor discharge temps

    Hi Welder
    Not to sure about the other refrigerants but I was taught (when I was younger) for R22, 12 or 502 the rule of thumb was around 21°C above ambient for the condensing temp. I'm sure some members could give an example range for the others for general ambient conditions how ever extreme ambients could differ a little.

  6. #6
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: compressor discharge temps

    Quote Originally Posted by Tesla View Post
    Hi Welder
    Not to sure about the other refrigerants but I was taught (when I was younger) for R22, 12 or 502 the rule of thumb was around 21°C above ambient for the condensing temp. I'm sure some members could give an example range for the others for general ambient conditions how ever extreme ambients could differ a little.
    Tesla,

    You really can a rule of thumb only because for the same condensing temperature if the suction pressure is equivalent at 0ºC it will be xxºC of discharge temperature; now if it is -30ºC it will be a bigger bigger discharge temperature.
    To make progress is never good enough, I want to do better and better and better

  7. #7
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: compressor discharge temps

    You really can call a rule of thumb only...
    To make progress is never good enough, I want to do better and better and better

  8. #8
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    52
    Posts
    1,083
    Rep Power
    23

    Re: compressor discharge temps

    Sandro Baptista I only wrote a general rule of thumb for gerneral conditions and it can be applied to varying evap temps. As these three gases have their temp ranges - low, med and high. With your age you should know this as a general rule of thumb. Welder is asking what the expected cond temps are and I have written what I would expect for one of the gases. Can we not give what might be expected for the other gases for general conditions even if there may be exceptions?

  9. #9
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: compressor discharge temps

    Tesla, he asked about discharge temperature and it varies a lot with the operating conditions that's why we should indicate a range of temperatures. If he want more accurancy then he should gives precise parameters.

    Even if he asked about expected condensing temperature that's depends on the weather conditions and condenser selection criteria. In conclusion that could vary a lot.
    To make progress is never good enough, I want to do better and better and better

  10. #10
    Join Date
    Sep 2009
    Location
    uk
    Posts
    14
    Rep Power
    0

    Re: compressor discharge temps

    ok Suction 5 deg ambient 12 deg?

  11. #11
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: compressor discharge temps

    12ºC ambient...what's the condensing temperature you want to use? it depends on the DT.
    To make progress is never good enough, I want to do better and better and better

  12. #12
    Join Date
    Sep 2009
    Location
    uk
    Posts
    14
    Rep Power
    0

    Re: compressor discharge temps

    27? condensing

  13. #13
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: compressor discharge temps

    -5ºC(saturated temperature)/+27ºC(saturated temperature) measure at inlet and outlet of the compressor.

    Considered type of compressor: piston

    R22 » +55ºC
    R407C » +60ºC
    R410A » +50ºC

    Hope this helps
    Note: Approximate temperatures. suction superheated temperature considered = 6K
    To make progress is never good enough, I want to do better and better and better

  14. #14
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: compressor discharge temps

    Quote Originally Posted by Tesla View Post
    Sandro Baptista I only wrote a general rule of thumb for gerneral conditions and it can be applied to varying evap temps. As these three gases have their temp ranges - low, med and high. With your age you should know this as a general rule of thumb. Welder is asking what the expected cond temps are and I have written what I would expect for one of the gases. Can we not give what might be expected for the other gases for general conditions even if there may be exceptions?
    General rule of thumb would be 20-30K and not 21K exactly.

  15. #15
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: compressor discharge temps

    With those refrigerants listed I would assume that you are looking mainly at AC equipment.

    If you are worried about the maximum temperatures then compare notes with the manufacturers fault finding instructions.

    When you get to the page with F??, High Discharge Temperature, it will give you the tripping temperature.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  16. #16
    Join Date
    Sep 2009
    Location
    uk
    Posts
    14
    Rep Power
    0

    Re: compressor discharge temps

    Ok thanks gents.I have checked the unit suction is 0 discharge is 50 C ,ambient is 8.6 c.R22 Does that sound about right?

  17. #17
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: compressor discharge temps

    It seems okay comparing with the preview discharge temperatures indicated and having in account that the pressure ration is a little less.
    To make progress is never good enough, I want to do better and better and better

Similar Threads

  1. LPG Chest Freezer Heat element temps?
    By errant in forum Technical Speculations
    Replies: 10
    Last Post: 22-01-2010, 10:21 PM
  2. Compressor oil temps
    By Superfridge in forum Industrial Compressors
    Replies: 5
    Last Post: 17-11-2009, 08:35 PM
  3. OPen grab and go case wierd temps
    By kengineering in forum Technical Discussions
    Replies: 22
    Last Post: 01-03-2008, 12:21 PM
  4. Extra Horsepower From Cooling Intake Temps
    By BigJon3475 in forum Technical Speculations
    Replies: 14
    Last Post: 12-07-2007, 01:37 AM
  5. R410A split min and max line temps
    By smileypete in forum Domestic
    Replies: 1
    Last Post: 17-11-2005, 10:38 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •