    In Parallel Rack do you separate tubes for each Evaporator?



    Hello!

    When using a Parallel Compressor Rack (*****), do you use (1) cooper tube for each Evaporator from the Manifold or do you use a single bigger tube and connect it to several Evaporatos?

    I've seen both but can't get a reason to use one or other.

    Thanks!



  2. #2
    Join Date
    Feb 2010
    Location
    England
    Age
    60
    Posts
    242
    Rep Power
    16

    Re: In Parallel Rack do you separate tubes for each Evaporator?

    Quote Originally Posted by georgedvf View Post
    Hello!

    When using a Parallel Compressor Rack (*****), do you use (1) cooper tube for each Evaporator from the Manifold or do you use a single bigger tube and connect it to several Evaporatos?

    I've seen both but can't get a reason to use one or other.

    Thanks!
    Both..

    Where I'm from the one tube is called a ring main (one liquid suplying many evaps).

    The other is the stub type.

    One suply for each individual section.

    The one pipe (ring main) is the most popular nowadays and has replaced the individual stub system.

    Cost will be the biggest reason.
    To run the single pipe (ring main) it uses less copper tubing
    so will be cheaper to install.

    All the best

    coolrunnings

    .

  3. #3
    Join Date
    Oct 2007
    Location
    Mexico
    Age
    44
    Posts
    158
    Rep Power
    17

    Re: In Parallel Rack do you separate tubes for each Evaporator?

    Thanks coolrunnings.

    And if I use the "ring main" solution, how do I design correctly the pipe diameter considering that each Evaporator has solenoid valve to stop when temperature is achieved or to defrost individually?

    I forgot, Do you use this solution in suction line too?

    Thanks!
    Last edited by georgedvf; 25-01-2011 at 11:51 PM.

  4. #4
    Join Date
    Feb 2009
    Location
    Australia
    Posts
    272
    Rep Power
    16

    Re: In Parallel Rack do you separate tubes for each Evaporator?

    georgedvf,
    With freezers here i use stubs from each evaporator to the rack where i fit Sporlan Sorit valves for temp control and shutdown for defrosting,the liquid solenoid is only for defrost,temp control by the sorit(pressure)Lawrie
    Remember we are here for a good time, not a long time.
    Trust me i'm a Fridgy.

  5. #5
    Join Date
    Oct 2007
    Location
    Mexico
    Age
    44
    Posts
    158
    Rep Power
    17

    Re: In Parallel Rack do you separate tubes for each Evaporator?

    Thanks Lawrence1, Do you only use stubs on freezers? Is there a technical reason to do that?

    Thanks!

  6. #6
    Join Date
    Feb 2009
    Location
    Australia
    Posts
    272
    Rep Power
    16

    Re: In Parallel Rack do you separate tubes for each Evaporator?

    georgedvf,
    No we use stubs on all racks (low temp and medium temp)
    Remember we are here for a good time, not a long time.
    Trust me i'm a Fridgy.

  7. #7
    Join Date
    Oct 2007
    Location
    Mexico
    Age
    44
    Posts
    158
    Rep Power
    17

    Re: In Parallel Rack do you separate tubes for each Evaporator?

    Is there a technical reason for you to not use a ring mains?

    Thanks!

  8. #8
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: In Parallel Rack do you separate tubes for each Evaporator?

    Quote Originally Posted by georgedvf View Post
    Hello!

    When using a Parallel Compressor Rack (*****), do you use (1) cooper tube for each Evaporator from the Manifold or do you use a single bigger tube and connect it to several Evaporatos?

    I've seen both but can't get a reason to use one or other.

    Thanks!
    I use one liquid tube and one suction tube. But if there are many evaporators (big capacity) than some times I prefer to divide suction tube on two tubes, because diameter of one tube too big and it cost more expensive than two smaller...
    In some places will have to think ...

  9. #9
    Join Date
    Jul 2001
    Location
    Sydney, Australia
    Posts
    753
    Rep Power
    25

    Re: In Parallel Rack do you separate tubes for each Evaporator?

    I'd look to find a happy medium, basically you need to assess the total load - lets say its 150kw MT load

    I would look at what the maximum I could put on one 2 and 1/8 ring main - to do this you really need to map out the pipework on a drawing and have some idea of distances and pipe routing, you should be able to squeeze somewhere around 40kw of MT load on to each main without too much pressure drop - I like to work off 1 to 1.5k Maximum. This would mean you will be looking at 4 x 2-1/8" ring main suction lines on that 150kw load, but you really need to assess each bit of pipework for pressure drop.

    It is far cheaper to run ring mains however low load scenarios need to be taken into account especially when sizing vertical lines (risers), installation time is cut by about 25 to 30% on ring mains as it is physically less sets of pipes but a lot more care and attention needs to go into sizing and installation practices.
    ...and she said "give it to me you big fridgie"

  10. #10
    Join Date
    Oct 2007
    Location
    Mexico
    Age
    44
    Posts
    158
    Rep Power
    17

    Re: In Parallel Rack do you separate tubes for each Evaporator?

    Thanks 750 Valve!

    And what about liquid lines, is there a special consideration to design diameters when using ring mains? When low load scenario the velocity drops enormously, this is critical in liquid lines? Ashrae books only says that liquid lines should have 1.5m/s or less (how much less???).

    Thanks!

  11. #11
    Join Date
    Jul 2001
    Location
    Sydney, Australia
    Posts
    753
    Rep Power
    25

    Re: In Parallel Rack do you separate tubes for each Evaporator?

    Low velocity is not usually an issue in liquid lines, and I would be looking at cond drain lines in the vicinity of 0.5m/s max = nice big drain line
    ...and she said "give it to me you big fridgie"

  12. #12
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: In Parallel Rack do you separate tubes for each Evaporator?

    Quote Originally Posted by georgedvf View Post
    Thanks 750 Valve!
    Ashrae books only says that liquid lines should have 1.5m/s or less (how much less???).
    According to Braidert recomendations, velocity in liquid pipe should be in interval of 0.3-1.2 m/s.
    In condencer drain line velosity should be less than 0.5 m/s (like 750 Valve said).
    In some places will have to think ...

Similar Threads

  1. Solenoid Valves in Parallel Compressors Rack System
    By georgedvf in forum Technical Speculations
    Replies: 40
    Last Post: 18-08-2010, 12:59 PM
  2. hot idle compressor on parallel rack system
    By friocold2008 in forum Supermarket Refrigeration
    Replies: 11
    Last Post: 05-12-2009, 08:37 AM
  3. parallel evaporator again
    By alkum in forum Legal-Business-Marketing
    Replies: 1
    Last Post: 22-11-2009, 10:46 PM
  4. Parallel rack compressor leak
    By racknovice in forum Supermarket Refrigeration
    Replies: 7
    Last Post: 03-09-2007, 07:41 PM
  5. ***** parallel compressor rack systems
    By COLD WANG in forum Commercial
    Replies: 30
    Last Post: 20-12-2006, 06:21 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •