    Trane chiller RTAC250 Alarm



    Hi All,
    I have alarm with Trane chiller RTAC250 The alarm is " Starter Did not Transition - cprsr 1B" and this alarm shutdown the compressor 1B when it tries to start up i have no idea about this alarm what is the reason and what is it mean. two weeks ago all the compressors of chiller work properly. So what can i do to solve this problem?

    Thanks & Regards



  2. #2
    Join Date
    Oct 2010
    Location
    Greece
    Age
    52
    Posts
    97
    Rep Power
    14

    Re: Trane chiller RTAC250 Alarm

    Hi Cool King 2007,
    You should check the integrity of all contactors coils and if the auxiliary contacts are having good contact with contactors.
    Most probably you have to change all auxiliary contacts, but you can also check their wiring.
    Regards,
    CV
    Attached Files Attached Files
    • File Type: pdf 1.pdf (21.2 KB, 27 views)

  3. #3
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Trane chiller RTAC250 Alarm

    Quote Originally Posted by CV_Geardrive View Post
    Hi Cool King 2007,
    You should check the integrity of all contactors coils and if the auxiliary contacts are having good contact with contactors.
    Most probably you have to change all auxiliary contacts, but you can also check their wiring.
    Regards,
    CV
    Hi that is good advice i would follow it!
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

Similar Threads

  1. Carrier Transicold Container Problem
    By Shamel in forum Transport
    Replies: 39
    Last Post: 23-01-2012, 11:23 PM
  2. Dunham Bush Chiller Alarm
    By Regulator in forum Air Conditioning
    Replies: 11
    Last Post: 08-12-2010, 01:42 AM
  3. unloading Trane RTHA chiller
    By aumeche96 in forum Commercial
    Replies: 1
    Last Post: 21-10-2010, 05:26 AM
  4. Replies: 3
    Last Post: 13-06-2009, 01:39 PM
  5. Trane CVHE 450 R11 Centrifugal Chiller
    By albertjoseph in forum Air Conditioning
    Replies: 4
    Last Post: 06-10-2008, 03:23 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •