Results 1 to 3 of 3
  1. #1
    koekoeh's Avatar
    koekoeh Guest

    Problem Latched fault Trane RTA 125



    We got problem on start Y delta, on chiller trane RTA 125.
    Problem : Latched fault n Phase reversal Prot lost.

    We have changed contactor all, but the problem still there.
    pls advise what I have to check to solve this problem.

    thanks for your help.



  2. #2
    Join Date
    Oct 2010
    Location
    Greece
    Age
    52
    Posts
    97
    Rep Power
    14

    Re: Problem Latched fault Trane RTA 125

    Hi Koekoeh,
    Most probably you should change all auxiliary contacts of affective compressor contactors.
    If you need detailed answer please provide more data.
    1. Model number. It is RTAA or RTAD or…??
    2. Is this happening in both compressors?
    3. What is the sequence before the unit fails? Does it start at Y and trips on transition mode or in D mode?
    4. Is it happening always or only when the other compressor is in operation.
    5. Etc….
    In each case provide details in order to have a valid answer.
    Regards,
    CV
    Attached Files Attached Files
    • File Type: zip 1.zip (81.5 KB, 54 views)

  3. #3
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Problem Latched fault Trane RTA 125

    HI i would check the voltage transformers that provide the unit with phase rotation warning.you should also check the ct's.
    good luck
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

Similar Threads

  1. Trane CVHG problem
    By iceman007 in forum Commercial
    Replies: 1
    Last Post: 30-12-2009, 11:34 PM
  2. problem with GE air con power problem
    By Richie101 in forum Air Conditioning
    Replies: 6
    Last Post: 05-11-2009, 04:00 PM
  3. Samsung Vivace Problem AQV24VBCN
    By goldpau in forum Air Conditioning
    Replies: 0
    Last Post: 18-09-2009, 06:28 PM
  4. Trane JUAC0125B problem
    By LRAC in forum Air Conditioning
    Replies: 2
    Last Post: 28-10-2008, 08:52 PM
  5. Fault with Tango cassette
    By airefresco in forum Air Conditioning
    Replies: 8
    Last Post: 19-09-2007, 08:42 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •