Problem Latched fault Trane RTA 125
We got problem on start Y delta, on chiller trane RTA 125.
Problem : Latched fault n Phase reversal Prot lost.
We have changed contactor all, but the problem still there.
pls advise what I have to check to solve this problem.
thanks for your help.
-
25-01-2011, 05:46 AM #2
Re: Problem Latched fault Trane RTA 125
Hi Koekoeh,
Most probably you should change all auxiliary contacts of affective compressor contactors.
If you need detailed answer please provide more data.
1. Model number. It is RTAA or RTAD or…??
2. Is this happening in both compressors?
3. What is the sequence before the unit fails? Does it start at Y and trips on transition mode or in D mode?
4. Is it happening always or only when the other compressor is in operation.
5. Etc….
In each case provide details in order to have a valid answer.
Regards,
CV
-
26-01-2011, 02:10 PM #3
Re: Problem Latched fault Trane RTA 125
HI i would check the voltage transformers that provide the unit with phase rotation warning.you should also check the ct's.
good luckTHE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!
Similar Threads
-
Trane CVHG problem
By iceman007 in forum CommercialReplies: 1Last Post: 30-12-2009, 11:34 PM -
problem with GE air con power problem
By Richie101 in forum Air ConditioningReplies: 6Last Post: 05-11-2009, 04:00 PM -
Samsung Vivace Problem AQV24VBCN
By goldpau in forum Air ConditioningReplies: 0Last Post: 18-09-2009, 06:28 PM -
Trane JUAC0125B problem
By LRAC in forum Air ConditioningReplies: 2Last Post: 28-10-2008, 08:52 PM -
Fault with Tango cassette
By airefresco in forum Air ConditioningReplies: 8Last Post: 19-09-2007, 08:42 AM