    gavin g's Avatar
    gavin g Guest
    fujitsu flash codes
    i have a fujitsu ASTA09JCC indoor unit with active codes.
    the red and green LED's flash together twice then the red LED will flash on its own foiur more times.
    please help
    Dec 2010
    Australia
    Re: fujitsu flash codes
    Hi There, In regard to your fault code it doesnt sound familiar. Two lights flash then four times? Are you sure thats right? I have all the fault code listings for Fujitsu in regard to inverters and not one matches up..four flashes is a PFC fault which is the power factor controller which regulates the power in the circuit which is part of the main controller board in the outdoor unit. Have you got the Red LED on the outdoor unit on/flashing?
    Dec 2010
    Australia
    Also If the Red operation light flashes four times you could be looking at an indoor unit power interruption...But i need more info to be more certain cheers mate
    Sep 2010
    Kazakhstan
    36
    Maybe Timer (Green) - 2 times blink
    and Operation (Red) - 6 times blink.
    It is - indoor fan motor lock error.
    Some info from Fujitsu. Look p.02-02 and p.02-14 here: http://www.goductless.com/v/vspfiles...lq_service.pdf
    Apr 2006
    stafford
    42
    974
    see attached, not sure if it is relevant to your model
    Attached Files Attached Files
    Paul
    "KEEP IT COOL"
    emjay's Avatar
    emjay Guest
    according to fujitsu error contents, 6 red + 2 green flashes indicates indoor fan motor, abnormal lock.
    gavin g's Avatar
    gavin g Guest
    Quote Originally Posted by emjay View Post
    hi, yes you are right!
    the indoor fan is U/S
    Thanks heaps for the help.
    Gavin G
  1. YORK split air conditioner Code error F6
    By Jean in forum Air Conditioning
    Last Post: 13-12-2010, 02:17 PM
  2. Fujitsu AST18LSBCW error codes
    By gllitznz in forum Heat Pumps
    Last Post: 15-06-2010, 11:39 PM
  3. York A/C fault code needed
    By Yuri B. in forum Air Conditioning
    Last Post: 17-08-2009, 11:19 PM
  4. fujitsu fault codes
    By Andy AC in forum Air Conditioning
    Last Post: 06-03-2009, 02:38 PM