    Toshiba RAV series L29 fault??



    I was called to a site with a unit showing this fault, reset unit and ran away fine for about 5 hours, cut out on same fault. Toshiba tech support wasnt in the office so he couldn't help. I checked a few other units in the building and they showed the same fault in the memory. Can anyone help?

    Thanks



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Toshiba RAV series L29 fault??

    L29 Error on outdoor unit, etc.
    · Communication error between
    CDB and IPDU
    (Coming-off of connector)
    · Heat sink temperature
    error
    (Temperature over specified
    value was detected.)
    1. CDB and IPDU wiring cables check
    2. Abnormal overload operation of refrigerating cycle


  3. #3
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Toshiba RAV series L29 fault??

    Error on outdoor unit, etc.
    · Communication error between
    CDB and IPDU
    (Coming-off of connector)
    · Heat sink temperature
    error
    (Temperature over specified
    value was detected.)

    1. CDB and IPDU wiring cables check
    2. Abnormal overload operation of refrigerating
    cycle
    The difference between genius and stupidity is that genius has its limits.

    Marc

  4. #4
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Toshiba RAV series L29 fault??

    Install Monkey you beat me to it
    The difference between genius and stupidity is that genius has its limits.

    Marc

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Toshiba RAV series L29 fault??

    mark5180 beat by 2 mins haha-we must have the same library of manuals

  6. #6
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Toshiba RAV series L29 fault??

    It looks that way doesn't it
    The difference between genius and stupidity is that genius has its limits.

    Marc

  7. #7
    Join Date
    Mar 2008
    Location
    Ireland
    Age
    39
    Posts
    9
    Rep Power
    0

    Re: Toshiba RAV series L29 fault??

    Ambint temp where condensers are located is about 40 Celsius so over temp of heat sink sounds to be right. I'll check all the other possibilities too. That fact that other units have had same fault is a clue too. Thanks for you help guys

  8. #8
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Toshiba RAV series L29 fault??

    check the condenser coils are clean and put some systems in heating to lower the ambient around condensers,also ensure the inverter cooling fins are clean too

Similar Threads

  1. Toshiba Fault codes
    By bernard in forum Air Conditioning
    Replies: 28
    Last Post: 03-08-2010, 11:09 AM
  2. toshiba a/c fault codes
    By fsfd1 in forum Trouble Shooting
    Replies: 1
    Last Post: 30-09-2008, 07:10 PM
  3. toshiba fault codes
    By COOL BOB in forum New to RE
    Replies: 7
    Last Post: 09-12-2007, 08:18 AM
  4. Toshiba a/c fault codes
    By Latte in forum Air Conditioning
    Replies: 3
    Last Post: 27-09-2007, 09:33 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •