Thread: Toshiba RAV series L29 fault??
-
24-01-2011, 10:02 PM #1
Toshiba RAV series L29 fault??
I was called to a site with a unit showing this fault, reset unit and ran away fine for about 5 hours, cut out on same fault. Toshiba tech support wasnt in the office so he couldn't help. I checked a few other units in the building and they showed the same fault in the memory. Can anyone help?
Thanks
-
24-01-2011, 10:11 PM #2
Re: Toshiba RAV series L29 fault??
L29 Error on outdoor unit, etc.value was detected.)
· Communication error between
CDB and IPDU
(Coming-off of connector)
· Heat sink temperature
error
(Temperature over specified
1. CDB and IPDU wiring cables check
2. Abnormal overload operation of refrigerating cycle
-
24-01-2011, 10:13 PM #3
Re: Toshiba RAV series L29 fault??
Error on outdoor unit, etc.
· Communication error between
CDB and IPDU
(Coming-off of connector)
· Heat sink temperature
error
(Temperature over specified
value was detected.)
1. CDB and IPDU wiring cables check
2. Abnormal overload operation of refrigerating
cycleThe difference between genius and stupidity is that genius has its limits.
Marc
-
24-01-2011, 10:14 PM #4
Re: Toshiba RAV series L29 fault??
Install Monkey you beat me to it
The difference between genius and stupidity is that genius has its limits.
Marc
-
24-01-2011, 10:15 PM #5
Re: Toshiba RAV series L29 fault??
mark5180 beat by 2 mins haha-we must have the same library of manuals
-
24-01-2011, 10:16 PM #6
Re: Toshiba RAV series L29 fault??
It looks that way doesn't it
The difference between genius and stupidity is that genius has its limits.
Marc
-
24-01-2011, 10:39 PM #7
Re: Toshiba RAV series L29 fault??
Ambint temp where condensers are located is about 40 Celsius so over temp of heat sink sounds to be right. I'll check all the other possibilities too. That fact that other units have had same fault is a clue too. Thanks for you help guys
-
24-01-2011, 10:53 PM #8
Re: Toshiba RAV series L29 fault??
check the condenser coils are clean and put some systems in heating to lower the ambient around condensers,also ensure the inverter cooling fins are clean too
Similar Threads
-
Toshiba Fault codes
By bernard in forum Air ConditioningReplies: 28Last Post: 03-08-2010, 11:09 AM -
toshiba a/c fault codes
By fsfd1 in forum Trouble ShootingReplies: 1Last Post: 30-09-2008, 07:10 PM -
toshiba fault codes
By COOL BOB in forum New to REReplies: 7Last Post: 09-12-2007, 08:18 AM -
Toshiba a/c fault codes
By Latte in forum Air ConditioningReplies: 3Last Post: 27-09-2007, 09:33 PM