Loss of Phase Current
Hello, I have a Trane Chiller rtaa 216.
It was running fine till about a 1/2 year ago.
Now it's tripping on:Loss of Phase Current.
I checked the compressorwindings with a ohmmeter,the current transformers and the cables.
I also checked the contacters.
Can anyone give a hint on what to do next?
-
24-01-2011, 07:56 PM #2
Re: Loss of Phase Current
Check and tighten wiring connections. A poor connection will overheat, so an IR thermometer can be very useful for this.
-
24-01-2011, 08:43 PM #3
Re: Loss of Phase Current
Hi Cubecool.
Gary's advise is sound.
What is happening is there is no current being sensed on one or more of the current transformer inputs.
So I would check the obvious, if you have not already done so.
That there is a phase supply to each of the run contactors.
Just in case a line fuse has not blown?
Secondly with the power off do you get continuity across the contactor terminals. Are there any signs of the overheating Gary mentions.
Thirdly if voltages are OK then check out your CT coils.
From what you describe something has failed, you just need to identify what.
Good Luck Grizzly
-
25-01-2011, 08:34 AM #4
Re: Loss of Phase Current
Hi Cubecool,
Some units have double HP switches.
Check external and internal reset of HP switch.
You can also place a jumper (for test purpose) to HP switch to check if the compressor starts or not.
You can also check or replace all auxiliary contacts of compressors contactors and you can check if the contactors coils are OK.
If not, please let us know following:
1. Is part winding or Y-D?
2. If part winding has a 0,5 seconds timer or not?
3. Year of manufacturing.
Regards,
CV
-
25-01-2011, 08:52 AM #5
Re: Loss of Phase Current
Thanks guys,
I checked the contacts of both the main contactors and
replaced the starpoint contactor.
I also checked the voltage to the contactors.
Could there be something wrong in the controllboard?
I wiil check your remarks as soon as I get to the chiller.
-
25-01-2011, 10:12 AM #6
Re: Loss of Phase Current
Only a stab in the dark, ( not familiar with model #)
Is it a screw or a scroll? does it have a phase rotation /failure module? could there be a problem with that?
Just thinking out loud.
-
25-01-2011, 10:16 AM #7
Re: Loss of Phase Current
I think you could have a voltage unbalance that causes one phase to draw more current. Check and report back to us accordingly.
-
25-01-2011, 02:41 PM #8
Re: Loss of Phase Current
a very common problem on these machines is that the auxiliary contacts do not confirm the start of the compressor and this is read by the module and phase loss
-
26-01-2011, 02:04 PM #9
Re: Loss of Phase Current
Hi i have had to replace the control board ,it has the current inputs and might of blown a diode,
i wouldnt change this board unless you narrow it down to that,check your ct's
and check your inputs on the card.
good luckTHE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!
Similar Threads
-
Carrier Transicold Container Problem
By Shamel in forum TransportReplies: 39Last Post: 23-01-2012, 11:23 PM -
Trouble understanding a/c current in relation to a single phase supply.
By mburns in forum FundamentalsReplies: 16Last Post: 08-12-2010, 07:56 AM -
SR2 50 models electric SBY diagonostics made simple
By absolute-zero in forum TransportReplies: 5Last Post: 04-01-2008, 05:11 PM -
Operating 60 cycle scroll compressor with 50 cycle 3 phase current
By megavac in forum CommercialReplies: 5Last Post: 09-08-2007, 01:29 AM -
Phase Loss Detection
By Latte in forum New TechnologiesReplies: 37Last Post: 03-01-2005, 10:01 PM