Results 1 to 10 of 10
Thread: Thermometer
    Aug 2003
    London uk
    23
    Thermometer
    Can you please let me know what thermometer you are using to measure superheat in a walk-in freezer.
    I have been using a multi-meter with a type K thermister adaptor measuring pipe surface temperature but at –20ºC the multi-meter (fluke) does not seem to give stable readings.
    I have looked into other electronic thermometers but they are all rated at an ambient of <0ºC. Infrared thermometers have the same problem.
    Any suggestions would be appreciated
    Mark
    Oct 2008
    mallorca, spain,
    75
    768
    Re: Thermometer
    hi mbreward,
    I have for a long time had a RS206 -3738 c+f , hold button, t1 and t2 plus plastic cover< which I put on the thermometer upsidedown to cover the readout screen.
    happy testing, sedgy,
    Aug 2007
    Sydney
    52
    1,083
    23
    Re: Thermometer
    Hi mbreward
    you could use a superheat calculation kit where the thermometer measures the direct temp of the refrigerant.
    It is not a stable measurement - it is dynamic and due to the flow and constant adjusting of the metering device. The one is use is about 10 years old and it would be good if a manufacturer would build one that gives a K value with average, min and max readings. I use the yellow jacket ritchie.
    I spoke with a boss from CPS in the USA last year and he said they were working on an electronic diagnosis tool which also did data logging.
    0°C is a standard calibration temp I think the next standard is around 28°C (mercury) so 0°C is the closest for calibration for measuring superheat. I also have a fluke with a high digit resolution but have found they are not accurate and the range is too high.
    Aug 2003
    London uk
    23
    Re: Thermometer
    Thanks Sedgy
    Can you tell me what probes you use
    Jun 2009
    Lusk , Dublin
    1,115
    Re: Thermometer
    Hey Lads
    I was constantly having trouble with readings from various manufacturers thermometers and found i was wasting money constantly buying new ones (although i now possess quite the collection)
    In the end i bit the bullet and bought a yellow jacket system analyser.Real time superheat and subcooling graphable readings
    and Monitoring capabilities all downloadable for client presentation.
    A bit pricey but in my opinion well worth it .Has paid for itself over and over in time saved.
    The only thing i did was replace the k-type leads with 2 clamp on probes from my combustion test kit.
    It cost E800 and software upgrades are free from the Yellow Jacket site after registration(which is free)
    Stu
    http://www.yellowjacket.com/node/928
    Tool's ? check ! Condom's ? check !
    Aug 2007
    Sydney
    52
    1,083
    23
    Re: Thermometer
    stufus
    Wow that is really cool and just what I have been looking forward to, thank you and of course I had faith in Yellow Jacket all these years. Just to be sure are there any other members that have a better product that we should know about before we spend the money?
    Stu (Tesla)
    Oct 2008
    mallorca, spain,
    75
    768
    Re: Thermometer
    hi mbreward, yes I used 2x binda pointed sensors. Velcro held sensors, handheld surface sensor and a couple of 5 meter cable sensors< with bare wire ends< hope this helps
    sedgy
    Aug 2003
    London uk
    23
    Re: Thermometer
    Thanks for your suggestions, I'll look into both of them, the Yellow jacket superheat testing kit looks very good & reading the refrigerant temperature must be better than the pipe surface temperature
    thanks again
    Mark
    Jun 2009
    Lusk , Dublin
    1,115
    Re: Thermometer
    Quote Originally Posted by mbreward View Post
    thanks again
    Mark
    Have a look at the Testo Manifold range seem to be popular with some members.Only used them once so not to familiar with them but do remember saying "when i earn a decent wage i'll invest in one of these"
    But alas went on the piss instead
    Stu
    Jan 2006
    Croatia
    68
    2,263
    31
    Re: Thermometer
    I was using Testo 560-2 Refrigeration System Analyzer (for ammonia and other 30-40 max refrigerants ) good instrument .... can be connected to PC to store data etc...etc... quite expensive was that one about 2500E+ ... of course with wire and radio temp probes, SS flexible hoses...
    Best regards, Josip
  1. Discharge thermometer
    By jbuhler in forum Fundamentals
    Last Post: 23-09-2010, 06:37 PM
  2. Calibration of thermometer
    By samisonfire in forum Tools and Calculators
    Last Post: 25-04-2010, 11:52 AM
  3. Cold Room Dead Spots and thermometer readings
    By tudorice in forum Technical Discussions
    Last Post: 21-10-2009, 09:54 PM
  4. Randell refrigrator needs new thermometer
    By BlueVanACD2005 in forum Commercial
    Last Post: 09-11-2007, 02:17 PM
  5. Non contact thermometer
    By reefertech in forum Technical Discussions
    Last Post: 18-06-2005, 03:29 AM