    ASHP to heat a greenhouse!!? Will it work?



    Hello guys,
    In your expert opionins, could an ASHP be used to heat a greenhouse? The one in question was previously connected to an oil boiler, this fed two 4" steel pipes which run the entire length of the greenhouse (approx 25meters!!) and then return on themselves and go back to the boiler ( reduced to 1.1/2 tappings)
    Would an ASHP be man enough!?? Im thinking of the volume of water in these pipes must be massive!
    Thoughts!???



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: ASHP to heat a greenhouse!!? Will it work?

    Like any heat source or cooling source, to be effective, they need to be sized to match the heat loss or gain.

    If you can provide us with the amount of heat loss from the greenhouse (kW) at the worst outdoor winter conditions, then we might be able to answer your question.

    There is a lot of science to this business but not a lot of guessing. To be of any help to you we need information to work with.

    Do you have access to anyone that can provide some numbers?

    ASHP's can be connected in tandem to provide varying duties so it just might be possible. 4" pipes sound like a big system though
    Last edited by frank; 21-01-2011 at 09:06 PM.

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: ASHP to heat a greenhouse!!? Will it work?

    Any idea what the duty of the oil boiler was?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    pentium's Avatar
    pentium Guest

    Re: ASHP to heat a greenhouse!!? Will it work?

    Afraid not, the oil boiler was removed many years ago!
    My calculations suggest there is approx 800 litres of water to be heated in 100 meters of 4" pipework!?? Does this sound right, or have i messed up there!?
    The heat loss of a greenhouse, where does one start with u values on that!??

  5. #5
    Join Date
    Dec 2010
    Location
    Ireland
    Posts
    339
    Rep Power
    15

    Re: ASHP to heat a greenhouse!!? Will it work?

    Quote Originally Posted by pentium View Post
    Hello guys,
    In your expert opionins, could an ASHP be used to heat a greenhouse? The one in question was previously connected to an oil boiler, this fed two 4" steel pipes which run the entire length of the greenhouse (approx 25meters!!) and then return on themselves and go back to the boiler ( reduced to 1.1/2 tappings)
    Would an ASHP be man enough!?? Im thinking of the volume of water in these pipes must be massive!
    Thoughts!???
    Volume of water or size of piping is not the issue. Its the temperature of the water thats critical. If these 4" pipes are currently carrying 60-70C water then you will never match that duty with an ASHP. Your heat emitter would need to be much larger and work at a lower temp.

  6. #6
    Join Date
    Dec 2010
    Location
    Ireland
    Posts
    339
    Rep Power
    15

    Re: ASHP to heat a greenhouse!!? Will it work?

    Quote Originally Posted by pentium View Post
    Afraid not, the oil boiler was removed many years ago!
    My calculations suggest there is approx 800 litres of water to be heated in 100 meters of 4" pipework!?? Does this sound right, or have i messed up there!?
    The heat loss of a greenhouse, where does one start with u values on that!??
    You'd need to find the U value of the glass, the indoor temp you expect and the minimum outdoor temp.

    Tbh unless you have scope to fit a ufh system to this greenhouse then this would be a non runner imo. You can't put more heat emitters at height as this will restrict sunlight, so heating from the bottom up with the storage a screed would provide is the only way this will work.

    We designed something like this for mushroom tunnels a few years back, the project didn't progress, but that was how we had planned on doing it

  7. #7
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: ASHP to heat a greenhouse!!? Will it work?

    I suppose one question is, how hot do you want this greenhouse?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  8. #8
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,492
    Rep Power
    24

    Re: ASHP to heat a greenhouse!!? Will it work?

    OK, look on the ends of the piping and see if there are any steam traps present. Many many systems in old green houses did use steam to keep the piping to a minimum so if this is/was the case you could be looking at replacing 100-105C heating temps. Some were changed from the steam to high temp water and there might be some evidence of the change.

  9. #9
    nevgee's Avatar
    nevgee is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2006
    Location
    Yorkshire
    Age
    72
    Posts
    420
    Rep Power
    18

    Re: ASHP to heat a greenhouse!!? Will it work?

    K value of glass is 1.05 W/mC

    "U" value of typical single glazing with metal frames, approx 20% framing could easily be between 5.0 and 6.7 W/m2C in severe conditions. Standard glass is 6 mmm I think where as greenhouse glass is 4mm.

    Gives some idea for a rough calc.

    Q = area x U x dt

    Then there will be the vent rate to consider which could be quite high.

    Question to ask is the heating required for frost protection during cold spells or to be a heated house for growing exotics etc.
    Reality is an elusion created by alcohol deficiency. Quaff and enjoy. [Yorkshire, UK]

  10. #10
    Join Date
    Nov 2006
    Location
    UK
    Age
    50
    Posts
    712
    Rep Power
    23

    Re: ASHP to heat a greenhouse!!? Will it work?

    Is a green house not the same as a conservatory

  11. #11
    Join Date
    Nov 2010
    Location
    Germany
    Age
    39
    Posts
    120
    Rep Power
    14

    Re: ASHP to heat a greenhouse!!? Will it work?

    I have an excel spreadsheet for a heat load calculation for green houses..Can i attach it somehow, i have tried but nothing happened
    Be careful about reading health books. You may die of a misprint.

  12. #12
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: ASHP to heat a greenhouse!!? Will it work?

    Quote Originally Posted by MilosBog View Post
    I have an excel spreadsheet for a heat load calculation for green houses..Can i attach it somehow, i have tried but nothing happened
    So long as it is not above the forum limits for attachments, Just reply to a post and then scroll down to 'Manage Attachments'

  13. #13
    Join Date
    Nov 2010
    Location
    Germany
    Age
    39
    Posts
    120
    Rep Power
    14

    Re: ASHP to heat a greenhouse!!? Will it work?

    Don have an idea ...it just refuses to attach the file..

    in Short, homogeneous losses are standard U*DT*A and than this value must be multiplied with some correction factors . One factor is F1=1.12 and i dont have an idea what is about, the Buderus guys have told me. The second factor is F2=1/111662.531*Atot+0.8560445 .
    So than we have a transmision heat loss
    Qtr=F1*F2*U*DT*A.
    Infiltration losses-how many air is to be changed and some values are here
    Construction SystemAir Exchanges/ Hour 1.
    New construction, glass or fiberglass 0.75 to 1.5 2.
    New construction, double layer PE 0.50 to 1.0 3.
    Old construcyion, glass, good maintenance 1.00 to 2.0 4.
    Old construction, glass, poor condition 2.00 to 4.0

    The total loads are sum of infiltration loads and transmission.
    Be careful about reading health books. You may die of a misprint.

  14. #14
    Join Date
    Nov 2010
    Location
    Germany
    Age
    39
    Posts
    120
    Rep Power
    14

    Re: ASHP to heat a greenhouse!!? Will it work?

    Maybe if the water content is enough,sufficient amount of energy can be stored..Please check firstly the load, and next what could be done. In my case i have had a problem with the soil, the constant soil temperature had to be maintained so PEX pipes where installed. Than the heat output was non constant due to the moisture of the soil.....
    Be careful about reading health books. You may die of a misprint.

  15. #15
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: ASHP to heat a greenhouse!!? Will it work?

    Yeah this could be done with an air source heat pump but like all of the other posts the capacity required and the flow temp for design is required. The main problem with the site would be that the power supply is most likely not going to be big enough.
    Have you thought about a Rotex solar boiler to take advantage of the solar gain during the day? How much power is on site?

  16. #16
    Join Date
    Jun 2005
    Location
    California
    Posts
    395
    Rep Power
    19

    Re: ASHP to heat a greenhouse!!? Will it work?

    The majority of plants grown in greenhouses thrive best at temperatures between 50 and 85 degrees Fahrenheit. Depending on the style, geographic location and desired interior atmosphere of the greenhouse
    Some other things to consider
    Insulating a greenhouse is simple.Adding insulation to a greenhouse is an inexpensive way to help maintain a steady temperature throughout the year; insulation becomes especially important in winter, when heating a greenhouse can become very costly. Use bubble wrap and silver-lined insulation to get the best results when insulating the interior portion of your greenhouse. Put insulation around the exterior portion of the greenhouse to add extra warmth to the building and help give it a constant temperature, no matter what the season.You can also tape bubble wrap to windows in addition, I found this study at
    http://cat.inist.fr/?aModele=afficheN&cpsidt=15780008
    .

Similar Threads

  1. MVHR with Heat Pump Recovery - Reduced Defrost
    By Pincher in forum Heat Pumps
    Replies: 10
    Last Post: 08-03-2011, 10:21 PM
  2. Prison vs Work
    By Abe in forum Chit Chat & Service Stories
    Replies: 11
    Last Post: 06-09-2010, 08:47 PM
  3. Pool heat pump water side diagram
    By nike123 in forum Heat Pumps
    Replies: 23
    Last Post: 22-03-2009, 08:42 PM
  4. Asthma at work
    By Abe in forum Legal-Business-Marketing
    Replies: 3
    Last Post: 12-06-2008, 07:11 PM
  5. Heat transfer coefficient - Coolpack
    By Graham in forum Fundamentals
    Replies: 10
    Last Post: 28-05-2008, 01:08 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •