    Exclamation compressor cut out ?????



    Hey fellas im working on an airdale v41d u64525
    its comprised of 2 outdoor units, obviously with 2 compressors inside, now the problem is one of the compressors keeps tripping out,now iv checked the pressures suction is 66 psi, discharge is 225 psi as they should be
    checked voltage thats fine
    compressor is drawing between 10- 15 running amps
    and windings are about 1.2 its really cold up here so if fan speed was too high could this be the problem any advive would be great its 2 o clock on a friday ... the pub is calling, cheers lads



  2. #2
    Join Date
    Jun 2009
    Location
    wales, cardiff
    Age
    37
    Posts
    70
    Rep Power
    15

    Re: compressor cut out ?????

    sorry guys running amp at compressor 10 amps

  3. #3
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: compressor cut out ?????

    hi andy ,
    and what is the overload set at?
    what gas are we on ? are we on heating or cooling ? whats the room temp? whats the set temp.? hum controle?

  4. #4
    Join Date
    Jun 2009
    Location
    wales, cardiff
    Age
    37
    Posts
    70
    Rep Power
    15

    Re: compressor cut out ?????

    r407c
    LP = 6 psi out-40 psi in
    HP = 385 psi out-man reset
    in constant cooling
    room temp 21 deg
    humidity min 30 max 100 %
    deadband humidity min 2 max 20 %
    it has alarm for humidity on digin control no fault showing
    Last edited by andyc425; 21-01-2011 at 03:57 PM.

  5. #5
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: compressor cut out ?????

    hi andy, just trying to establish the reason why one con,d unit is tripping ?
    you say the room is 21c= ok whats the set temp? < is the room down to temp and so its dropped put stage 2 cooling ?
    or < you say one comp, is tripping out <on what ? if its a standard airedale there is only the comp, overload to hold off the comp, only
    on the outgoing side of the comp, contactor there will be an overload conected to the contactor by three prongs being held by three screws , on the side of the o-L there is adjustable plastic arrow to set the maximum amps the comp, will run at, so if the comp is taking 10 amp the overload must be set over that set point,
    or is the suspect comp, feel very hot? hope you find the reason . sedgy

  6. #6
    Join Date
    Dec 2010
    Location
    devon
    Age
    53
    Posts
    837
    Rep Power
    24

    Re: compressor cut out ?????

    on that airdale one unit is cooling one controls humidity whats the indoor a scirroco? whats it tripping on signal?

  7. #7
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: compressor cut out ?????

    Have you megger'd the windings? Could be tripping under certain conditions if the readings are not in excess of 2M ohms.

    And don't rule out that the MCB (breaker)for the compressor is faulty

  8. #8
    Join Date
    Jun 2009
    Location
    wales, cardiff
    Age
    37
    Posts
    70
    Rep Power
    15

    Re: compressor cut out ?????

    cheers for your replies lads,
    i will check amp overload setting
    i have already checked resistance on comp windings its 1.2 ohms
    triple checked mcb
    although im not that familiar with heater strip on outside of compressor it was boiling to touch possible cause, id say yes but as i said limited exp on crankcase heaters.also sedgy the compressor it knocking of prematurley and not because of 2 stage cooling it alarms on digin controll with no detailed description,do yoy think possible safety circuit is sticking open which is linked in line with comp?

  9. #9
    Join Date
    Mar 2006
    Location
    belfast
    Posts
    239
    Rep Power
    19

    Re: compressor cut out ?????

    have 4 comp rooms with airdale units and at least 1 unit in each room tripped on this when we had a bad cold spell

    on start up suction pressure was pulling down then comming back up to normal

    a few times it hit low pressure settings

    suspect this as snow ice build up around condensers

  10. #10
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: compressor cut out ?????

    test the insulation to earth with a megohm meter-less than 1mohm is earth leakage resistance of the windings will only show open circuit or an inbalance in the windings.test the contactor hasnt got pitted contacts as this can give a higher running current

  11. #11
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: compressor cut out ?????

    Quote Originally Posted by andyc425 View Post
    cheers for your replies lads,
    i will check amp overload setting
    i have already checked resistance on comp windings its 1.2 ohms
    triple checked mcb
    although im not that familiar with heater strip on outside of compressor it was boiling to touch possible cause, id say yes but as i said limited exp on crankcase heaters.also sedgy the compressor it knocking of prematurley and not because of 2 stage cooling it alarms on digin controll with no detailed description,do yoy think possible safety circuit is sticking open which is linked in line with comp?
    Checking the resistance of the windings is not the same as checking the windings with a megger (insulation resistance to earth)
    Out of interest, how did you test the MCB and determine that it was OK?

  12. #12
    Join Date
    Jun 2009
    Location
    wales, cardiff
    Age
    37
    Posts
    70
    Rep Power
    15

    Re: compressor cut out ?????

    i checked the voltage on each mcb the compressor was linked to which was 2 three point 240v mcbs. plus i checked the current to and from both mcbs up until the comp,also the earth onside of compressor was visually fine but no i didnt check earth resistance just checked windings 1 to 2 ,1-3 etc , Monkey i have never encountered inbalance before what should i look for an how do i rectify also my suspicion was safety circuit stuck open but without an electrical diagram i am stumped to what is linked it could be so many things
    im back in tomorrow il have another crack at it then thanks all for your replies much appreciated.
    cheers fellas
    Last edited by andyc425; 23-01-2011 at 11:25 PM.

  13. #13
    Join Date
    Jun 2009
    Location
    wales, cardiff
    Age
    37
    Posts
    70
    Rep Power
    15

    Re: compressor cut out ?????

    i dont no how but it is now working everything seems fine for the moment cheers guys, like suggested probably safety circuit stuck open.