    York Air Cooled Screw Compressor Burned



    Hi All Expert,

    The problem as showed below:

    a) 2 phase short with earth on the compressor when i used the mega to test.

    b) Star-delta starter also become black color on the cable terminal.

    c) Oil level sensor & heater melt.

    d) whole body of the compressor become very hot. (Estimated more than 150'C)

    e) It's tripped to main incoming.

    From the above condition, who can advise what is the root cause to make this happen?

    Do you think the star-delta starter willl cause the compressor burned?

    Thank you



  2. #2
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: York Air Cooled Screw Compressor Burned

    Quote Originally Posted by Eddylim View Post
    Hi All Expert,

    The problem as showed below:

    a) 2 phase short with earth on the compressor when i used the mega to test.

    b) Star-delta starter also become black color on the cable terminal.

    c) Oil level sensor & heater melt.

    d) whole body of the compressor become very hot. (Estimated more than 150'C)

    e) It's tripped to main incoming.

    From the above condition, who can advise what is the root cause to make this happen?

    Do you think the star-delta starter willl cause the compressor burned?

    Thank you
    There are 1001 ways this could of burnt out, chicken and egg, comes to mind (cause and effect)
    For example, if two the Star delta contactor array had siezed (welded closed) then this would cause the motor to burn, but you said you had a short to earth, this short (in rush) could weld the contacts on your star delta array.
    If you are going to rewind the comp, makes sure you also complete a mechanical inspection (as mechanical problems end up showing as electrical problems)
    "If in doubt, biff it out"
    Last edited by mad fridgie; 20-01-2011 at 02:12 AM.

  3. #3
    Join Date
    Jan 2008
    Location
    India
    Age
    70
    Posts
    171
    Rep Power
    17

    Re: York Air Cooled Screw Compressor Burned

    York uses multi strand cable termination with out lugs which most ofthe time gets loose contact and the flash over occurs.We had a chiller at Colombo where the flash over had happened within six months of installation

Similar Threads

  1. York screw
    By riksly in forum Fundamentals
    Replies: 4
    Last Post: 26-08-2010, 06:55 PM
  2. York Screw Model YCASO330
    By James K. Donell in forum Technical Speculations
    Replies: 1
    Last Post: 12-06-2010, 11:24 PM
  3. YORK Rotary Screw Compressor
    By xelazman in forum Industrial Compressors
    Replies: 7
    Last Post: 28-04-2010, 08:37 PM
  4. York ycas air cooled screw
    By Dazzle in forum Trouble Shooting
    Replies: 1
    Last Post: 24-12-2009, 01:38 PM
  5. York Screw Oil Problem
    By tomt in forum Technical Discussions
    Replies: 10
    Last Post: 02-12-2009, 02:48 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •