    Copeland Scroll in reversable heat pump



    Hi, I have a Water to Water heat pump with a copeland scroll compressor, In heating the compressor works fine suction 6-9Bar and discharge around 25-30 bar, the problem is when i reverse it to put it in cooling mode the compressor sound like its going to shake itself to bits in cooling the suction is 9bar and the discharge is 10bar, is there an issue with the suction and discharge being so close?



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Copeland Scroll in reversable heat pump

    Your reversing valve is faulty and it bypass partially suction and discharge of compressor in cooling mode.
    Last edited by nike123; 19-01-2011 at 12:38 PM.

  3. #3
    Geothermal's Avatar
    Geothermal Guest

    Re: Copeland Scroll in reversable heat pump

    Hi Nike, Thanks for the reply, i have checked the operation of the reversing valve, it does operate ok but im not sure if its sealing 100% i will look at this again, do you know if running the compressor at very close suction and discharge pressures will cause an issue? Thanks

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Copeland Scroll in reversable heat pump

    Quote Originally Posted by Geothermal View Post
    Hi Nike, Thanks for the reply, i have checked the operation of the reversing valve, it does operate ok but im not sure if its sealing 100% i will look at this again, do you know if running the compressor at very close suction and discharge pressures will cause an issue? Thanks
    Yes, it will overheat.

    It is definitely 4-way valve if compressor is noisy and pressures are close, and in same time, in heating mode everything is fine.
    Last edited by nike123; 19-01-2011 at 12:42 PM.

  5. #5
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Copeland Scroll in reversable heat pump

    Quote Originally Posted by Geothermal View Post
    Hi Nike, Thanks for the reply, i have checked the operation of the reversing valve, it does operate ok but im not sure if its sealing 100% i will look at this again, do you know if running the compressor at very close suction and discharge pressures will cause an issue? Thanks
    Hi:
    take nike123 advice and use it! he gave you the best advice!!AND FOR FREE you can check the four way valve, by simply checking the temps on the pipes!
    good luck
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

Similar Threads

  1. Design heat pump for a pool
    By rolandh in forum Heat Pumps
    Replies: 10
    Last Post: 23-09-2010, 10:50 AM
  2. New Heat Pump Forum
    By Argus in forum Heat Pumps
    Replies: 17
    Last Post: 10-04-2010, 09:12 AM
  3. Calorex 510 Heat pump question
    By jugglerb in forum Heat Pumps
    Replies: 8
    Last Post: 21-06-2009, 10:49 AM
  4. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM
  5. Will this heat pump work?
    By goodguy in forum Heat Pumps
    Replies: 7
    Last Post: 08-03-2008, 04:14 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •