    indoor coil freezing when system is not running



    Hello everyone i'm having trouble with a daikin R407c vrv system (2 pipe). unfortunatly i cant tell you the model as the name plate as been weathered and unable to read.
    Anyway a client of mine is complaining about two of the units that are fed from this system whats happining is the indoor coil is freezing over and leaking, having first checked the filters which were fine then checking system pressure which again is fine i'm at a loss as to why!
    Any over fault ie stat would send a fault signal to the remote.
    Then speaking to the client, she then told me both indoor units where not even switched on when this happened, which as you can imagine brought a blank expression to my face.
    Can this happen??????
    I wouldn't have thought so but if there is anyone out there that can shed a bit of light over this matter it would be very much appreciated.
    This is my first thread so look forward to what you guys have to say.
    Regards Andy



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: indoor coil freezing when system is not running

    How did you manage to check the system pressures and confirm that they were OK?

    I would suspect that the 2 fan coils showing signs of freezing up may have faulty eev's

  3. #3
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21

    Re: indoor coil freezing when system is not running

    you have faulty eevs try changing the heads over with a unit that is working it is userly the head not the hole valve

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: indoor coil freezing when system is not running

    is the contactor welded on the condenser?
    isolate condenser the power up the compressor shouldnt start straight away-usually a 3-5 min delay

  5. #5
    Join Date
    Mar 2010
    Location
    England
    Posts
    41
    Rep Power
    0

    Re: indoor coil freezing when system is not running

    This does sound like an EEv issue. If a VRV indoor unit in cooling reaches set point - 1 degree, expansion valves closes, so does not allow refrigerant to flow into coil. Failure of the valve is apparent if the units are off, but freeze up occurs, expansion valve will also remain fully closed. You can reset the expansion valve heads by powering the unit down and swapping the yellow and blues wires in the plug, then power up the unit for 5 seconds, power off again, then back up for a further 5 seconds. Power down and then swap the yellow and blue wires back to original position. Swapping these cables will fully back seat the pin in the valve coil, so when the unit is powered back up, the software will fully close the valve (+ 50 pulses to ensure closure). Operate the system with the units off and see if refrigerant still passes into them, if it does, then you will need to change them.

  6. #6
    andymccc's Avatar
    andymccc Guest

    Re: indoor coil freezing when system is not running

    Thanks for that guys, will give it a whirl.

    Thanks again

  7. #7
    Join Date
    Feb 2009
    Location
    USA
    Age
    54
    Posts
    143
    Rep Power
    16

    Re: indoor coil freezing when system is not running

    I read it too fast, but seems like a leaking solenoid valve, not sure if your system has one, but if it does...replace it.

  8. #8
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: indoor coil freezing when system is not running

    Quote Originally Posted by Mentallist View Post
    This does sound like an EEv issue. If a VRV indoor unit in cooling reaches set point - 1 degree, expansion valves closes, so does not allow refrigerant to flow into coil. Failure of the valve is apparent if the units are off, but freeze up occurs, expansion valve will also remain fully closed. You can reset the expansion valve heads by powering the unit down and swapping the yellow and blues wires in the plug, then power up the unit for 5 seconds, power off again, then back up for a further 5 seconds. Power down and then swap the yellow and blue wires back to original position. Swapping these cables will fully back seat the pin in the valve coil, so when the unit is powered back up, the software will fully close the valve (+ 50 pulses to ensure closure). Operate the system with the units off and see if refrigerant still passes into them, if it does, then you will need to change them.
    Very good and informative post.
    Many thanks Grizzly.
    Rep points added.

  9. #9
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: indoor coil freezing when system is not running

    yeah definitely an EEV body jammed.

Similar Threads

  1. using home AC system as a freezer
    By steve thailand in forum Air Conditioning
    Replies: 10
    Last Post: 18-06-2010, 10:02 PM
  2. Moisture in system
    By Debonair Spain in forum Trouble Shooting
    Replies: 21
    Last Post: 27-04-2009, 09:13 PM
  3. High Liquid Line Temperature
    By airefresco in forum Commercial
    Replies: 37
    Last Post: 11-02-2009, 04:36 PM
  4. Enthalpy Increasing Buffer System
    By Reflexive in forum Technical Speculations
    Replies: 3
    Last Post: 23-12-2008, 03:18 PM
  5. Refrigeration system proposal; comments please.
    By DaBit in forum Technical Speculations
    Replies: 13
    Last Post: 01-01-2003, 03:42 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •