Armstrong air purgers are a pain & expensive if needle & seat leak on air release mechanism.
There is an add on to rectify very easily & I am not sure if its only being done in Australia & who actually invented modification, but it works.
-Add on is basically plug off air release connection with 1/4" plug.
-Remove relief valve on top if instaled (1/2")
-Screw in Parker stainless steel LLC float switch
-In outlet of LLC float screw in a tee , with one branch of tee re-instal relief valve & other branch of tee screw in a solonoid (small as possible) followed by needle valve & check valve.
-Bracket if necassary
-Wire up solonoid in series with float switch .
Takes several hours & finished. The only thing really to maintain is solonoid valve which you could instal a stop valve before it as well if you wanted to .
Everything is screwed type fitting
-
18-01-2011, 08:00 PM #2
Re: Armstrong air purger modification
I much prefer the Hansen purger over the old armstrong.
-
18-01-2011, 08:33 PM #3
Re: Armstrong air purger modification
TXiceman,
Could'nt agree more but years ago there was'nt anything else out there.
It would be rare to put in a new one these days.
-
28-02-2011, 07:15 AM #4
Re: Armstrong air purger modification
Every amstrong i have worked on has leaked on the internal serpintine coil, as well as constant recomissioning
Hansen are plug n play, I prefer manual purging, unless there foul gas outlet is clocked by scada otherwise could hide a low side leak
-
06-05-2011, 07:43 AM #5
Re: Armstrong air purger modification
Hi all, I know the guy that did the first LLC float change. I have also converted the latest Hansen non electrical to float control, The factory needle and seat is a very poor design.
Similar Threads
-
Refrigerant loss from Hansen auto purger
By simplygold in forum NH3Replies: 4Last Post: 02-08-2010, 06:24 AM -
slide valve modification
By salamander in forum Industrial CompressorsReplies: 6Last Post: 20-02-2010, 11:08 AM -
Air source heat pump modification
By rt29781 in forum Heat PumpsReplies: 4Last Post: 23-12-2008, 08:41 AM -
What is the Basic Function of a Rapid Purger ?
By eng_ab in forum IndustrialReplies: 3Last Post: 11-06-2006, 07:53 PM