    3,356
    Armstrong air purger modification
    Armstrong air purgers are a pain & expensive if needle & seat leak on air release mechanism.
    There is an add on to rectify very easily & I am not sure if its only being done in Australia & who actually invented modification, but it works.
    -Add on is basically plug off air release connection with 1/4" plug.
    -Remove relief valve on top if instaled (1/2")
    -Screw in Parker stainless steel LLC float switch
    -In outlet of LLC float screw in a tee , with one branch of tee re-instal relief valve & other branch of tee screw in a solonoid (small as possible) followed by needle valve & check valve.
    -Bracket if necassary
    -Wire up solonoid in series with float switch .
    Takes several hours & finished. The only thing really to maintain is solonoid valve which you could instal a stop valve before it as well if you wanted to .
    Everything is screwed type fitting
    Mar 2005
    638
    Re: Armstrong air purger modification
    I much prefer the Hansen purger over the old armstrong.
    3,356
    TXiceman,
    Could'nt agree more but years ago there was'nt anything else out there.
    It would be rare to put in a new one these days.
    Feb 2010
    new zealand
    42
    67
    15
    Every amstrong i have worked on has leaked on the internal serpintine coil, as well as constant recomissioning
    Hansen are plug n play, I prefer manual purging, unless there foul gas outlet is clocked by scada otherwise could hide a low side leak
    Valentino's Avatar
    Valentino Guest
    Hi all, I know the guy that did the first LLC float change. I have also converted the latest Hansen non electrical to float control, The factory needle and seat is a very poor design.
  1. Refrigerant loss from Hansen auto purger
    By simplygold in forum NH3
    Last Post: 02-08-2010, 06:24 AM
  2. slide valve modification
    By salamander in forum Industrial Compressors
    Last Post: 20-02-2010, 11:08 AM
  3. Air source heat pump modification
    By rt29781 in forum Heat Pumps
    Last Post: 23-12-2008, 08:41 AM
  4. What is the Basic Function of a Rapid Purger ?
    By eng_ab in forum Industrial
    Last Post: 11-06-2006, 07:53 PM
