    dehumidifier evaporating temp



    Hi all.

    First of all, sorry for my english, i'm from Poland

    My question is only teoretical. Let say we have an air dryer, power from 25kW to 100kW, air flow through evaporator about 16000 m3/h.Air temp. 14deg. C.

    What is a good evaporating temperature? must it be above 0 deg. C to avoid evaporating freezing, or can it be for ex. -5 deg. C?



  2. #2
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: dehumidifier evaporating temp

    Temperature at any point of the coil shall never be below 0°C to avoid frosting.
    The best temperature is a compromise between compressor efficiency and dehumidification capacity.
    If you are designing a new system, you may need to tabulate compressor power input against dehumidification capacity, and find your best breakeven point.

  3. #3
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: dehumidifier evaporating temp

    It also depends on what relative humidity you want for a specific air temperature of the medium.

    The evaporating temperature could be a little below 0ºC with no problem giving you the possibility to increase the capacity of the cold coil.
    To make progress is never good enough, I want to do better and better and better

  4. #4
    Join Date
    Dec 2004
    Location
    LEBANON
    Age
    44
    Posts
    854
    Rep Power
    21

    Re: dehumidifier evaporating temp

    The evaporation tempreture should be below the dew point of the air to be treated.
    Depending on the design conditions, leave a deltaT of 5 degree between the dew point and the evaporation tempreture as a minimum difference , but make sure you are always positive.
    Engineering, sciences, math, physics and my brain will generate "not responding " soon

Similar Threads

  1. Evaporating pressure valve
    By civic9696 in forum Technical Discussions
    Replies: 0
    Last Post: 26-08-2010, 05:20 AM
  2. Replies: 5
    Last Post: 08-11-2009, 05:10 PM
  3. Temp. Rise at duct outlet
    By jwasir in forum Trouble Shooting
    Replies: 13
    Last Post: 10-05-2008, 04:22 PM
  4. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •