Thread: dehumidifier evaporating temp
-
17-01-2011, 02:42 PM #1
dehumidifier evaporating temp
Hi all.
First of all, sorry for my english, i'm from Poland
My question is only teoretical. Let say we have an air dryer, power from 25kW to 100kW, air flow through evaporator about 16000 m3/h.Air temp. 14deg. C.
What is a good evaporating temperature? must it be above 0 deg. C to avoid evaporating freezing, or can it be for ex. -5 deg. C?
-
17-01-2011, 03:22 PM #2
Re: dehumidifier evaporating temp
Temperature at any point of the coil shall never be below 0°C to avoid frosting.
The best temperature is a compromise between compressor efficiency and dehumidification capacity.
If you are designing a new system, you may need to tabulate compressor power input against dehumidification capacity, and find your best breakeven point.
-
17-01-2011, 04:00 PM #3
Re: dehumidifier evaporating temp
It also depends on what relative humidity you want for a specific air temperature of the medium.
The evaporating temperature could be a little below 0ºC with no problem giving you the possibility to increase the capacity of the cold coil.To make progress is never good enough, I want to do better and better and better
-
07-03-2011, 07:59 PM #4
Re: dehumidifier evaporating temp
The evaporation tempreture should be below the dew point of the air to be treated.
Depending on the design conditions, leave a deltaT of 5 degree between the dew point and the evaporation tempreture as a minimum difference , but make sure you are always positive.Engineering, sciences, math, physics and my brain will generate "not responding " soon
Similar Threads
-
Evaporating pressure valve
By civic9696 in forum Technical DiscussionsReplies: 0Last Post: 26-08-2010, 05:20 AM -
19XL High Discharge Temp intermittent alarm at compressor start
By pete_d in forum CommercialReplies: 5Last Post: 08-11-2009, 05:10 PM -
Temp. Rise at duct outlet
By jwasir in forum Trouble ShootingReplies: 13Last Post: 10-05-2008, 04:22 PM -
Compressor loading, cooling, and range of operation.
By Air duster in forum FundamentalsReplies: 10Last Post: 02-04-2008, 08:39 AM