    Hot Gas Defrost



    Installing a new system, just realised evaporator does not have electric heaters. its a 20 Kw evap

    So , Im going to have to go hot gas defrost

    The check valve.........does it go after the expansion valve

    Its better I look like an idiot asking, but I want to get it right

    Thx



  2. #2
    Join Date
    Jan 2005
    Location
    UK
    Age
    45
    Posts
    14
    Rep Power
    0

    Re: Hot Gas Defrost

    The chek valve should be installed parallel to TEV. The chek valve direction-to liquid line.

    Vaidas

  3. #3
    Join Date
    Jan 2005
    Location
    UK
    Age
    45
    Posts
    14
    Rep Power
    0

    Re: Hot Gas Defrost

    Ignore that I wrote above if your system has one compressor and evaporator. In that case you don't need the chek valve, if the liquid line has a solenoid of course.

  4. #4
    Join Date
    May 2004
    Location
    southern england
    Age
    69
    Posts
    86
    Rep Power
    20

    Re: Hot Gas Defrost

    If your system is a single evporator and unit, then you will not be able to use a two pipe hot or sat gas defrost method and will have to use a three pipe system. Take a 1/2 or 5/8 tee off the discharge and pipe (or top of reciever, if it contains enough volume of sat gas vapour to effect defrost) to a tee between the expansion device outlet and the distributor with a solenoid valve for control. The suction gas pressure to the compressor should be controlled with a crankcase pressure regulator. In practice it is a pretty crap way (Comp nearly always runs 100% of the time and eventually fails) of effecting a defrost and you would be far better to fit defrost heaters.
    it's only a fridge, fix it. ;)

  5. #5
    Join Date
    Jun 2005
    Location
    California
    Posts
    394
    Rep Power
    19

    Re: Hot Gas Defrost


  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Hot Gas Defrost

    Hi Wambat.

    The link doesn't work for me

  7. #7
    Join Date
    Dec 2004
    Location
    LEBANON
    Age
    44
    Posts
    854
    Rep Power
    21

    Re: Hot Gas Defrost

    I think that the link should be without the
    like this i think it will work http://www.sporlan.com/5-158.pdf , nothing should be after the final extension of a file , that's what's i've mentioned from my experience in computers
    Engineering, sciences, math, physics and my brain will generate "not responding " soon

  8. #8
    Join Date
    Dec 2001
    Location
    Cleveland
    Posts
    41
    Rep Power
    0

    Cool Re: Hot Gas Defrost

    Hello Aiyub

    The post the guys put up for you from Sporlan is NOT for defrost purposes this is for low load conditions/capacity control on a/c systems you would need more controls i.e. suction accumulator/pan loop/ solenoids/etc for defrost use

    regards
    Dave G

  9. #9
    Join Date
    Jun 2005
    Location
    California
    Posts
    394
    Rep Power
    19

    Re: Hot Gas Defrost

    Dave is correct, I believe this is better http://www.bmil.com/ballyrefrig/thermosaver.htm

  10. #10
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Hot Gas Defrost

    Hi mate,

    Is this a freezer application?
    My opinion, I should install heaters, vene if you have to remove the evaporator once again.
    Like the posters said, if it's a 1 evap/1 cond situation, you will also need to to install a TEV on your condensor and 2 check valves. A lot of work and the material will cost more than the heaters.
    In case of a reversal cycle, you will also need a large enough liquid separator.
    Otherwise your compressor will pump liquid after a defrost.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  11. #11
    Join Date
    Jan 2005
    Location
    UK
    Age
    45
    Posts
    14
    Rep Power
    0

    Re: Hot Gas Defrost

    Quote Originally Posted by Peter_1
    Hi mate,

    Is this a freezer application?
    My opinion, I should install heaters, vene if you have to remove the evaporator once again.
    Like the posters said, if it's a 1 evap/1 cond situation, you will also need to to install a TEV on your condensor and 2 check valves. A lot of work and the material will cost more than the heaters.
    In case of a reversal cycle, you will also need a large enough liquid separator.
    Otherwise your compressor will pump liquid after a defrost.
    Hi Peter, what do you mean "you will also need to to install a TEV on your condensor " and "In case of a reversal cycle, you will also need a large enough liquid separator"?

  12. #12
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27

    Re: Hot Gas Defrost

    Quote Originally Posted by Peter_1
    Hi mate,

    Is this a freezer application?
    My opinion, I should install heaters, vene if you have to remove the evaporator once again.
    Like the posters said, if it's a 1 evap/1 cond situation, you will also need to to install a TEV on your condensor and 2 check valves. A lot of work and the material will cost more than the heaters.
    In case of a reversal cycle, you will also need a large enough liquid separator.
    Otherwise your compressor will pump liquid after a defrost.
    Peter.

    Yes, it is a freezer room.

    Ive decided to install heaters, instead of going the hot gas defrost route

    I ordered 8 straight heater coils, cost £20.00 each. Total cost £160.00

    Fitted them today, now I dont have to worry about check valves and compressor burning out, etc

    Thanks for everyones help........I appreciate it.

    Abe

  13. #13
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Hot Gas Defrost

    Quote Originally Posted by vaidas_78
    Hi Peter, what do you mean "you will also need to to install a TEV on your condensor " and "In case of a reversal cycle, you will also need a large enough liquid separator"?
    http://www.bmil.com/ballyrefrig/thermosaver.htm is one example
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  14. #14
    Join Date
    Jan 2005
    Location
    UK
    Age
    45
    Posts
    14
    Rep Power
    0

    Re: Hot Gas Defrost

    Quote Originally Posted by Peter_1
    Sorry Peter, but I still can't see TEV on the condenser.All I can see is a 3-way solenoid valve.

  15. #15
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Hot Gas Defrost

    You're right, this wasn't a good example.
    This is a better one http://www.books4hvac.com/rb/Heat_Pumps1.htm
    I hadn't look very weel when I posted this link.
    They use a 3 way valve instead of a 4 way

    BTW, what do you guys think of the Thermosaver system?
    Two liquid separators, one with a succool coil in it.
    Why 2?
    Is the subcool coil in defrost mode acting as a small condensor?
    Where is the heat coming from to defrost the coil? Only from the absorbed power of the compressor?

    Where happens the expansion?
    What about excessive compressor SH?

    For smaller applications like small ice machines and small evaporators this will work fine but for the system like Aiyub, I doubt.
    Any comments on this?
    Last edited by Peter_1; 22-08-2005 at 10:15 AM.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  16. #16
    Join Date
    Jan 2005
    Location
    UK
    Age
    45
    Posts
    14
    Rep Power
    0

    Re: Hot Gas Defrost

    Hi Peter, it looks to me you have been confused.Thermosaver is not a heatpump and it use a 3way valve for defrosting, not for a cycle reversing.In this system the hot gas and a liquid are sharing the same pipe,so it needs 3way valve and two chek valves.
    The subcool coil in the defrost mode forces the liquid to boil in accumulator.
    The crankcase pressure regulator(pos.H) protects compressor from overloading during the defrost cycle and also evaporizes some liquid.

    Where is the heat coming from to defrost the coil?
    The vaporized refrigerant picks up some heat passing through the suction line. As it passes through the compressor, the heat of compression raises the temperature to such a level that it continues to heat the evaporator and remove the frost.

    Regards Vaidas

  17. #17
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Hot Gas Defrost

    Quote Originally Posted by vaidas_78
    .....,so it needs 3way valve and two chek valves.
    The subcool coil in the defrost mode forces the liquid to boil in accumulator.
    The crankcase pressure regulator(pos.H) protects compressor from overloading during the defrost cycle and also evaporizes some liquid.
    I hadn't noticed valve H, thought it was a shut-off valve.
    Valve H act while defrosting as an AEV.

    The vaporized refrigerant picks up some heat passing through the suction line. As it passes through the compressor, the heat of compression raises the temperature to such a level that it continues to heat the evaporator and remove the frost.
    I do understand the schematic, but you're confirming what I'm saying -I think- thermodynamically seen, the only heat we're adding to the system is the absorbed power of the compressor on that moment, which will very litlle due to the very small DP the compressor is working.
    Further more, the liquid coming from the evaporator encounters a serious temperature drop when entering the right accumulator (with the subcool coil)
    So the hot discharge gasses going to the evaporator for defrosting will undergo a serious cooling, so the net availbale heating effect will seriously decrease.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  18. #18
    Join Date
    Jan 2005
    Location
    UK
    Age
    45
    Posts
    14
    Rep Power
    0

    Re: Hot Gas Defrost

    Hi Peter,
    The main parameter for the discharge temperature(and also pressure) increasing is a compression ratio. Higher compression ratio - higher the temperature at the end of the compression.Low temperature compressors have the high compression ratio.What's why they cannot be used in high temperature aplications as a high suction pressure would increase the discharge temperature and pressure greatly.For this reason thermosaver is using the crankcase pressure regulator. During a defrost cycle DP is not very high but it's normal .Of course the suction gas temperature affects the discharge temperature but just slightly.
    What I don't like in this system is that the hot gas shares the same pipe with the liquid.At the beginnig of the defrost the hot gas will push the liquid all along the line and evaporator to the suction line.What's why they are using two liquid separators,I thik. What would happen if the liquid line would be very long?
    I would rather choose a three pipe system whith the one accumulator.
    What do you think?

Similar Threads

  1. Hot gas defrost
    By adam5365 in forum Transport
    Replies: 20
    Last Post: 04-11-2007, 06:23 AM
  2. Hot Gas defrost suction pressure regulation
    By 87mustang in forum Technical Speculations
    Replies: 5
    Last Post: 05-08-2005, 07:25 AM
  3. Hot Gas vs. Electric Defrost
    By herefishy in forum Technical Discussions
    Replies: 26
    Last Post: 08-03-2005, 07:50 PM
  4. Electric Defrost
    By iceman007 in forum Trouble Shooting