15-01-2011, 09:36 AM #1
should have been a plumber
Thanks sedgy.perhaps you could assist with another one? checking the temps on the liquid and suction i get 5 Deg (70psig) liquid 13 deg suction (92psig) so +7 accross the evap.Does that sound correct for R22 and what would you expect for 407 and 410a?
-
15-01-2011, 11:38 AM #2
Re: should have been a plumber
sorry welder , I am sure one of the mods will come on to tell you the correct answer to this one.
regards sedgy
-
15-01-2011, 01:42 PM #3
Re: should have been a plumber
Thanks anyway !! enjoy the sun.
Any mods got a reply?
-
15-01-2011, 01:51 PM #4
Re: should have been a plumber
Hi Welder
Sorry I'm not a mod but for hi temp application (ac) I would expect around 60 - 70 psi for r22 suction press. If you give us more detail on the system your working on we could help further. As for the r4XX I'm not sure but you could check on a pressure temp chart.
-
15-01-2011, 09:48 PM #5
Re: should have been a plumber
You need to use a refrigerant comparator to convert the temperatures to pressures.
For all high temp applications your saturated suction temp should be around 0C (depending on the load) wether you are using R22, R407c, R410a the temps stay the same yet the pressures differ which is why comparators are used.The difference between genius and stupidity is that genius has its limits.
Marc
Similar Threads
-
Uk young plumber of the year
By El Padre in forum Chit Chat & Service StoriesReplies: 2Last Post: 05-12-2010, 07:04 AM -
plumber to refrigeration engineer???
By rueben2288 in forum Air ConditioningReplies: 4Last Post: 05-01-2010, 07:12 PM -
Vaillant Air Conditioning
By Prince Vaillant in forum Air ConditioningReplies: 61Last Post: 02-08-2008, 08:03 PM -
Change of Job
By Brian_UK in forum Chit Chat & Service StoriesReplies: 49Last Post: 20-09-2003, 03:26 AM