    Thanks sedgy.perhaps you could assist with another one? checking the temps on the liquid and suction i get 5 Deg (70psig) liquid 13 deg suction (92psig) so +7 accross the evap.Does that sound correct for R22 and what would you expect for 407 and 410a?



  2. #2
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: should have been a plumber

    sorry welder , I am sure one of the mods will come on to tell you the correct answer to this one.
    regards sedgy

  3. #3
    Join Date
    Sep 2009
    Location
    uk
    Posts
    14
    Rep Power
    0

    Re: should have been a plumber

    Thanks anyway !! enjoy the sun.

    Any mods got a reply?

  4. #4
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    51
    Posts
    1,083
    Rep Power
    23

    Re: should have been a plumber

    Hi Welder
    Sorry I'm not a mod but for hi temp application (ac) I would expect around 60 - 70 psi for r22 suction press. If you give us more detail on the system your working on we could help further. As for the r4XX I'm not sure but you could check on a pressure temp chart.

  5. #5
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: should have been a plumber

    Quote Originally Posted by Welder View Post
    Thanks sedgy.perhaps you could assist with another one? checking the temps on the liquid and suction i get 5 Deg (70psig) liquid 13 deg suction (92psig) so +7 accross the evap.Does that sound correct for R22 and what would you expect for 407 and 410a?
    You need to use a refrigerant comparator to convert the temperatures to pressures.

    For all high temp applications your saturated suction temp should be around 0C (depending on the load) wether you are using R22, R407c, R410a the temps stay the same yet the pressures differ which is why comparators are used.
    The difference between genius and stupidity is that genius has its limits.

    Marc

Similar Threads

  1. Uk young plumber of the year
    By El Padre in forum Chit Chat & Service Stories
    Replies: 2
    Last Post: 05-12-2010, 07:04 AM
  2. plumber to refrigeration engineer???
    By rueben2288 in forum Air Conditioning
    Replies: 4
    Last Post: 05-01-2010, 07:12 PM
  3. Vaillant Air Conditioning
    By Prince Vaillant in forum Air Conditioning
    Replies: 61
    Last Post: 02-08-2008, 08:03 PM
  4. Change of Job
    By Brian_UK in forum Chit Chat & Service Stories
    Replies: 49
    Last Post: 20-09-2003, 03:26 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •