    Receiver to Discharge Balance Line



    Hi all

    Could some one please shed some light on sizing and installation of the HP receiver to discharge balance line.

    I have been reading the ASHRAE handbooks and now have a better understanding of this rather inportant component but could find no sizing data.

    Thanks in advance



  2. #2
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Receiver to Discharge Balance Line

    Someone may add correct method , but our engineers would say the bigger the better.
    A decent size plant would have anything from 50-80mm balance line.

    If t/syphon its bigger again , probably same size as main discharge header.

  3. #3
    Join Date
    Feb 2009
    Location
    Australia
    Posts
    272
    Rep Power
    16

    Re: Receiver to Discharge Balance Line

    On Supermarket racks we use a 5/8'' from the condenser to receiver with a check valve.
    Lawrie
    Remember we are here for a good time, not a long time.
    Trust me i'm a Fridgy.

  4. #4
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Receiver to Discharge Balance Line

    size is not important is is usually 1/2
    in NH3 and R and it is for balancing pressure in winter and summer times,
    in winter it is open (keep liquid in condenser to bring dawn capacity of condenser in winter and rise of discharge pressure)
    it is install discharge line goes to condenser and top of receiver with regulator valve (stop valve not recommended).
    Last edited by mbc; 16-01-2011 at 10:05 AM.

  5. #5
    Join Date
    May 2009
    Location
    New Zealand
    Posts
    141
    Rep Power
    15

    Re: Receiver to Discharge Balance Line

    Quote; "The vent line flow is from receiver to condenser when receiver temp is higher than condensing temp. Flow is from condenser to receiver when air temp around receiver is below condensing temp. Flow rate depends on temp difference as well as on the receiver surface area. Vent size can be calculated from this flow rate"


    This must only be the case when pressures are equal between condenser and receiver? A correctly designed system?

    Have also read "a check valve can be fitted in the direction of the condenser when piping configeration is "unknown" ie unknown pressure drops and/or velocity pressure entering line to receiver"

  6. #6
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Receiver to Discharge Balance Line

    http://www.irc.wisc.edu

    Superfridge,
    Please find link posted by Sergei .
    It has a download to calculate balance line. Unfortunately its in psi ,tons etc

  7. #7
    Join Date
    May 2009
    Location
    New Zealand
    Posts
    141
    Rep Power
    15

    Re: Receiver to Discharge Balance Line

    Thanks for the link RANGER1, a good find.

    I would like to know how to calculate the pipe sizing long hand/old school so if anyone know's and is prepared to share this valuable information..........

    My recent investigation has proven some of the plant I work on have this line incorrectly installed.
    Just go's to show that a plant can be in service for 20 odd years and still have fundamental improvements done.
    The comments like "it's always been like that" and "it always struggles in summer" now makes me think "let's have a closer look"

  8. #8
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Receiver to Discharge Balance Line

    There are a number of ways at looking at this.
    Sized upon max displacement,
    imagine you are pumping down (no liquid leaving the reciever) so to keep the system balanced, vapour has to be released back to the cond. So if you are inserting 1 litre of liquid, you must have to release one litre of vapour. You then need to know the length and height of the liquid and vapour balance, you need to ensure the presure drop is small to ensure flow.
    Or you could calculate the temp difference between the reciever and the cond, (how much energy is being absorbed by the reciever) Calculate how much flash gas is being produced, size you line again with little pressure drop.
    You could also condisider fitting a check valve in the liquid drop line. If there is a large difference between the reciever temp and the cond, then raising vapour can go up the dropper stopping liquid leaving the cond (liquid hung up!) add ing the check valve allows a liquid head to be produced over the check valve, allowing the pressure to equalize via the balancing line and allowing flow.

  9. #9
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Receiver to Discharge Balance Line

    Surerfridge try this , but the main problem will be connection size on liquid reciever.
    www.irc.wisc.edu/file.php?id=133

  10. #10
    Join Date
    May 2009
    Location
    New Zealand
    Posts
    141
    Rep Power
    15

    Re: Receiver to Discharge Balance Line

    Thanks again RANGER1,

    I see what you mean about the HP receiver connection size being a limiting factor.

    All good

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. sizing of equalising line receiver to condenser
    By davidlleida in forum Fundamentals
    Replies: 25
    Last Post: 02-02-2009, 07:19 PM
  3. Oil in discharge line
    By chillyblue in forum Trouble Shooting
    Replies: 18
    Last Post: 30-10-2008, 06:52 AM
  4. Exploded discharge line
    By Peter_1 in forum Industrial
    Replies: 1
    Last Post: 05-05-2004, 09:47 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •