    BS box to refnet minimum distance



    Gents

    Is there a minimum distance that Daikin BS boxes must be from the refnets?

    We have a VRVII which the piping has failed 5 times -which we put down to poor pipe- but now it's failed at the refnet so I am now leaning towards fatigue so wonder if the BS box being only 400mm is causing this to happen..

    We are going to replace the refnet and add a couple of loops to dampen out any stresses...

    Advice most welcome



  2. #2
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: BS box to refnet minimum distance

    1m if i remember correctly or it could be 500mm i dont have access to my daikin ioms at the moment but you can find them on the daikin extranet also the refnet Has to be within 30degrees of level (15 either way) this may be useful http://www.youtube.com/watch?v=3_TwScCzvUg

  3. #3
    Join Date
    Apr 2005
    Location
    Manchester England
    Age
    43
    Posts
    332
    Rep Power
    20

    Re: BS box to refnet minimum distance

    hi james thanks for that you tube clip you put up well worth a watch.

    cheers lee

  4. #4
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: BS box to refnet minimum distance

    Quote Originally Posted by james10 View Post
    1m if i remember correctly or it could be 500mm i dont have access to my daikin ioms at the moment but you can find them on the daikin extranet also the refnet Has to be within 30degrees of level (15 either way) this may be useful http://www.youtube.com/watch?v=3_TwScCzvUg

    Thanks james,

    I don't need the water vid thanks as the job is in and the refnets are installed properly just a bit close....

    I just like to know if there is a minimum. I have
    got this but it doesn't mention anything

    http://www.daikinac.com/commercial/d...-%20Daikin.pdf

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: BS box to refnet minimum distance

    piping failure-i gather u mean pipe fractures-if so loosen the pipe clips on the main run. in heating mode the pipe temperature causes linear expansion and then fractures.hydrazorb clips are renound for it.

  6. #6
    Join Date
    Nov 2010
    Location
    London
    Posts
    624
    Rep Power
    15

    Re: BS box to refnet minimum distance

    Quote Originally Posted by r.bartlett View Post
    Gents

    Is there a minimum distance that Daikin BS boxes must be from the refnets?

    We have a VRVII which the piping has failed 5 times -which we put down to poor pipe- but now it's failed at the refnet so I am now leaning towards fatigue so wonder if the BS box being only 400mm is causing this to happen..

    We are going to replace the refnet and add a couple of loops to dampen out any stresses...

    Advice most welcome
    This is a very interesting question. If the BS Box is mounted firm and the refnet is too, preventing radial movement, not necessarily preventing axial movement, and the pipe length between the two is short then I wonder if the pipe between the two could ever be too short to bow, so too short to deflect the forces of expansion, but expand enough to stress the refnet to failure.

    If multiple pipe repairs have taken place near that refent then maybe there just was accumulative stress from manually working the pipe in the location?
    Only the dogmatist says he will never change his mind. We all know that some of our opinions are wrong but none of us know which they are for if we did then they just wouldn't be our opinions. - JS Mill.

  7. #7
    Join Date
    Mar 2010
    Location
    England
    Posts
    41
    Rep Power
    0

    Re: BS box to refnet minimum distance

    There should a minimum straight length of 500mm of piping entering and exiting refnets. Im assuming the fractures you have suffered are in the discharge piping, be sure to check that you have the minimum straight lengths entering and exiting the refnet and ensure this field piping is not clipped excessively. Discharge piping can also be used as LP suction during full cooling operation, therefore temperatures in this pipe can range between 0 and anything up to and in excess of 100 degrees, therefore expansion and contraction can occur, if the piping is clipped too tight or excessively, fractures can occur at the refnet as this is the only allowable point of movement.
    Last edited by Mentallist; 13-01-2011 at 10:41 PM.

  8. #8
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: BS box to refnet minimum distance

    the first time I repaired it myself back in Dec 08. This wasn't installed by us as they use a national install contractor. (D1 but we won't go there!)

    See pic


    Can someone show me this 500mm as I can't find it anywhere and does it have to be 500mm straight. Can we have a loop (or two)

    See drawing
    Attached Images Attached Images

  9. #9
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: BS box to refnet minimum distance

    Found this, section 5, page 8 and fig 18-3.

    http://extranet.daikin.co.uk/en/docu...219-151019.pdf
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  10. #10
    Join Date
    Mar 2010
    Location
    England
    Posts
    41
    Rep Power
    0

    Re: BS box to refnet minimum distance

    Hi Richard, from the picture it looks as though the fracture is on a bend in the piping, when the bend is pulled this makes this section weaker than the straight sections, therefore, if there is no allowable movement in the piping to allow for expansion and contraction, the stress is is at the weakest part of the piping (The Bend) so fracture occurs. There is no reason why an expansion loop cannot be installed to prevent further failure. I have recommended this on sites before and it has cured issues such as this.

  11. #11
    Join Date
    Feb 2009
    Location
    Athens
    Age
    40
    Posts
    5
    Rep Power
    0

    Re: BS box to refnet minimum distance

    ok , i guarantee that the minimum lenght must be at least one meter distance from refnet to bs box , this is also written in the installation manual of the bs box or in the installation manual of the oudrood vrvII unit . except that , you shoud check if any liquid pipe is messed with an y air pipe (wrong side connections)).... Cheers .

Similar Threads

  1. Minimum Qualifications for UK Refrigeration Engineers
    By Abe in forum Legal-Business-Marketing
    Replies: 9
    Last Post: 28-07-2010, 07:44 PM
  2. Minimum distance to obstructions on entrance side of fan?
    By rooibos in forum Trouble Shooting
    Replies: 10
    Last Post: 21-08-2009, 02:53 PM
  3. VRV REFNET Joint
    By 2007eng in forum Air Conditioning
    Replies: 10
    Last Post: 03-08-2008, 07:17 PM
  4. Does distance affect capacity?
    By Dimitris in forum Technical Discussions
    Replies: 5
    Last Post: 12-03-2006, 02:49 PM
  5. refnet or T ?
    By cruzeiros in forum Air Conditioning
    Replies: 27
    Last Post: 01-03-2006, 05:13 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •