    I just installed a new 3 ton Grandaire 2H/1C heat pump in July with an off the shelf Honeywell Heat Pump T-stat from Home Depot. The HVAC tech who came out to my home noticed the T-stat was calling for AUX heat though the room temp was only 1 degree short(71) of the set temp(72). My Nov electric bill was $150 and my Dec electric bill was $230. We disconnected the white wires for the aux on the t-stat and off W2 on the air handler contacts. The unit has 140F degree suction temp so it doesn't need the aux heat even though it was 32F outside. The house heated just fine. The t-stat though was still calling for AUX though it was disconnected from the AUX on the contact board. What t-stat is rated for this heat pump? Also, has anyone heard of this or seen this happen, know the solution?
    Thanks!
    Matt



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Honeywell T-stat Unecessarily Calls for AUX Heat

    Which model thermostat is it, there are a lot of Honeywell models.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Dec 2010
    Location
    Arlington, VA, USA
    Age
    52
    Posts
    11
    Rep Power
    0

    Re: Honeywell T-stat Unecessarily Calls for AUX Heat

    Quote Originally Posted by Brian_UK View Post
    Which model thermostat is it, there are a lot of Honeywell models.

    It is Honeywell Model RTH2410 5-1-1 Programmable Thermostat

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Honeywell T-stat Unecessarily Calls for AUX Heat

    According to the manuals on the Honeywell site you seem to have a suitable stat as the RTH2410 5-1-1 is for a 2H/1C system.

    You can turn off the AUX option via the system set-up of the stat.

    edit: Forgot to say, the stat is designed to switch at 1°F from set point so it seems to be doing it's job.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Honeywell T-stat Unecessarily Calls for AUX Heat


  6. #6
    Join Date
    Dec 2010
    Location
    Arlington, VA, USA
    Age
    52
    Posts
    11
    Rep Power
    0

    Re: Honeywell T-stat Unecessarily Calls for AUX Heat

    Quote Originally Posted by Brian_UK View Post
    According to the manuals on the Honeywell site you seem to have a suitable stat as the RTH2410 5-1-1 is for a 2H/1C system.

    You can turn off the AUX option via the system set-up of the stat.

    edit: Forgot to say, the stat is designed to switch at 1°F from set point so it seems to be doing it's job.
    1. I would like to have aux heat when the outside temp dips down to about 15, guessing that would then require a little booster. Is there a way to set the lockout to kick the aux on @ 15? Also, since I am being told this AUX wire comes into play in the summer when cool call is made I need to wire this back up (not sure if this is true).

    2. I have the operator's manual and the Quick Installation guide but I don't have the advanced manual, how do I get that?

  7. #7
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Honeywell T-stat Unecessarily Calls for AUX Heat

    I used the manual given in Frank's link above.

    If after using the link you delete the last section of the link you should see more options.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  8. #8
    Join Date
    Dec 2010
    Location
    Arlington, VA, USA
    Age
    52
    Posts
    11
    Rep Power
    0

    Re: Honeywell T-stat Unecessarily Calls for AUX Heat

    Quote Originally Posted by Brian_UK View Post
    I used the manual given in Frank's link above.

    If after using the link you delete the last section of the link you should see more options.
    When I chop the end of the link I get errors.

Similar Threads

  1. Capacity control
    By sparrow in forum Training
    Replies: 44
    Last Post: 18-01-2010, 07:49 PM
  2. Replies: 5
    Last Post: 14-09-2009, 07:33 AM
  3. Basics or is it?
    By Fett in forum Fundamentals
    Replies: 17
    Last Post: 10-09-2009, 01:45 AM
  4. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM
  5. Low head pressure Versus Heat reclaim.
    By taz24 in forum Supermarket Refrigeration
    Replies: 17
    Last Post: 20-03-2008, 11:47 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •