    Suction values jumpin around
    Sabroe 163 mk compressor.the suction pressure and seq. suction pressure values are all over the place .Jumpin from for example 2 hg to 2 psi .Just changed tranducers cable and sensors but still happening .Anyone have an idea on what could be going on here ?
    Sep 2010
    United States
    32
    Re: Suction values jumpin around
    So far you have; Checked sensor location for oil, calibrated sensor and even installed a gauge beside it, replaced sensor and cable....and you are still getting problems. Did you zero out your Static offset? For example if you installed a 0 to 150# transducer.....input 0 for min and 150 for max?
    Nov 2009
    canada
    64
    15
    Quote Originally Posted by Terron View Post
    Yes i have none all of that ,cant understand whats going on here !
    Mar 2005
    638
    Has the transducer always done this or is it something new?
    Whet is the sensor located relative tot he sensing point?
    have you tried to throttle the block valve to the sensor?
    Have you confirmed the readings with a gauge ?
    It may be an electrically induced change and not mechanical. Is the cable properly grounded?
    It may be a problem with the point on the control board.
    Sep 2010
    United States
    32
    You did change like for like, for instance if it was a 1-6 volt transducer you replaced with 1-6 volt, not a 4 to 20 milli amp. and you said you did replace the wire so there couldn't be any rubbing issues there....And you positive you wired it up right? There really isn't anything trick about them. Is it coming off a three way valve? When did this problem occur? Have you had any electrical issues, (ie lightning storms)?
    Sep 2010
    United States
    32
    Who designed your control system?
    Nov 2009
    canada
    64
    15
    Quote Originally Posted by TXiceman View Post
    Has the transducer always done this or is it something new? yes but not so bad ,thats why we chnaged it out cuz we thought it was the trouble
    Whet is the sensor located relative tot he sensing point? on top of lpr
    have you tried to throttle the block valve to the sensor? YES
    Have you confirmed the readings with a gauge ? YES the gauge readings are right on
    It may be an electrically induced change and not mechanical. Is the cable properly grounded? YES I think electrically induced as well
    NOT sure.Cant seem to figure it out ,had a the electrician look at it and he said it could be electronic noise but we dont think thats it but could be
    Mar 2005
    638
    Put a mechanical gauge on it and see if it follows the transducer..pretty simple. If the guage is steady, them it is a problem with the electronics.
    Ken
    Nov 2009
    canada
    64
    15
    M&M refrigeration
    Sep 2010
    United States
    32
    That's what I thought, I will send you a contact number for M&M. He will be able to pin point a problem.
    Somerset
    69
    4,698
    Can someone tell me.
    Do M&M supply their own control software and Hardware or do they use the Sabroe Unisab Control system?
    Hi Stanthony.
    Is your pressure transducer a Danfoss AKS 32R as is supplied here in Europe.
    I may be able to help but because of size details I will have to email them to you, rather than post them.
    It's relatively easy to test the Signal / voltages from them.
    Nov 2009
    canada
    64
    15
    Hi Stanthony.
    Gauge pressure for seq. suction and compressor suction gauge reading are pretty much dead on when in sequenced mode.M&M is telling us to keep in sequenced mode while we r using just 1 compressor but i always figured you use seq mode when running 2 compressors .
    Sep 2010
    United States
    32
    Seq. mode removes each compressors micro panel reading and replaces it with the house reading. So they will all be reading the same suction pressures when staging on and off. Did you get the number I sent you?
    Sep 2010
    United States
    32
    So yes, you would tend to use it when running multiple compressors or a trim compressor.
    Sep 2010
    United States
    32
    Have you come any closer to solving your problem?
    Jan 2011
    GREECE
    8
    Chanche o rink in safety valve on comprecor
  1. Copeland select 6
    By Copman in forum Tools and Calculators
    Last Post: 27-05-2010, 09:01 PM
  2. R290 Suction Scrubber HI Level
    By Knappyfro in forum Trouble Shooting
    Last Post: 28-11-2009, 05:15 PM
  3. Location of Suction Filter
    By Ray123 in forum Fundamentals
    Last Post: 11-06-2009, 03:29 PM
  4. Replies: 0
    Last Post: 14-05-2008, 05:05 PM
  5. Benji