    Suction values jumpin around



    Hi,

    Sabroe 163 mk compressor.the suction pressure and seq. suction pressure values are all over the place .Jumpin from for example 2 hg to 2 psi .Just changed tranducers cable and sensors but still happening .Anyone have an idea on what could be going on here ?



  2. #2
    Join Date
    Sep 2010
    Location
    United States
    Posts
    32
    Rep Power
    0

    Re: Suction values jumpin around

    So far you have; Checked sensor location for oil, calibrated sensor and even installed a gauge beside it, replaced sensor and cable....and you are still getting problems. Did you zero out your Static offset? For example if you installed a 0 to 150# transducer.....input 0 for min and 150 for max?

  3. #3
    Join Date
    Nov 2009
    Location
    canada
    Age
    51
    Posts
    64
    Rep Power
    15

    Re: Suction values jumpin around

    Quote Originally Posted by Terron View Post
    So far you have; Checked sensor location for oil, calibrated sensor and even installed a gauge beside it, replaced sensor and cable....and you are still getting problems. Did you zero out your Static offset? For example if you installed a 0 to 150# transducer.....input 0 for min and 150 for max?
    Yes i have none all of that ,cant understand whats going on here !

  4. #4
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: Suction values jumpin around

    Has the transducer always done this or is it something new?

    Whet is the sensor located relative tot he sensing point?

    have you tried to throttle the block valve to the sensor?

    Have you confirmed the readings with a gauge ?

    It may be an electrically induced change and not mechanical. Is the cable properly grounded?

    It may be a problem with the point on the control board.

  5. #5
    Join Date
    Sep 2010
    Location
    United States
    Posts
    32
    Rep Power
    0

    Re: Suction values jumpin around

    You did change like for like, for instance if it was a 1-6 volt transducer you replaced with 1-6 volt, not a 4 to 20 milli amp. and you said you did replace the wire so there couldn't be any rubbing issues there....And you positive you wired it up right? There really isn't anything trick about them. Is it coming off a three way valve? When did this problem occur? Have you had any electrical issues, (ie lightning storms)?

  6. #6
    Join Date
    Sep 2010
    Location
    United States
    Posts
    32
    Rep Power
    0

    Re: Suction values jumpin around

    Who designed your control system?

  7. #7
    Join Date
    Nov 2009
    Location
    canada
    Age
    51
    Posts
    64
    Rep Power
    15

    Re: Suction values jumpin around

    Quote Originally Posted by TXiceman View Post
    Has the transducer always done this or is it something new? yes but not so bad ,thats why we chnaged it out cuz we thought it was the trouble

    Whet is the sensor located relative tot he sensing point? on top of lpr

    have you tried to throttle the block valve to the sensor? YES

    Have you confirmed the readings with a gauge ? YES the gauge readings are right on

    It may be an electrically induced change and not mechanical. Is the cable properly grounded? YES I think electrically induced as well

    It may be a problem with the point on the control board.
    NOT sure.Cant seem to figure it out ,had a the electrician look at it and he said it could be electronic noise but we dont think thats it but could be

  8. #8
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: Suction values jumpin around

    Put a mechanical gauge on it and see if it follows the transducer..pretty simple. If the guage is steady, them it is a problem with the electronics.

    Ken

  9. #9
    Join Date
    Nov 2009
    Location
    canada
    Age
    51
    Posts
    64
    Rep Power
    15

    Re: Suction values jumpin around

    Quote Originally Posted by Terron View Post
    Who designed your control system?
    M&M refrigeration

  10. #10
    Join Date
    Sep 2010
    Location
    United States
    Posts
    32
    Rep Power
    0

    Re: Suction values jumpin around

    That's what I thought, I will send you a contact number for M&M. He will be able to pin point a problem.
    Last edited by Terron; 12-01-2011 at 09:46 PM.

  11. #11
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: Suction values jumpin around

    Can someone tell me.
    Do M&M supply their own control software and Hardware or do they use the Sabroe Unisab Control system?

    Hi Stanthony.
    Is your pressure transducer a Danfoss AKS 32R as is supplied here in Europe.

    I may be able to help but because of size details I will have to email them to you, rather than post them.

    It's relatively easy to test the Signal / voltages from them.
    Grizzly

  12. #12
    Join Date
    Nov 2009
    Location
    canada
    Age
    51
    Posts
    64
    Rep Power
    15

    Re: Suction values jumpin around

    Quote Originally Posted by Grizzly View Post
    Can someone tell me.
    Do M&M supply their own control software and Hardware or do they use the Sabroe Unisab Control system?

    Hi Stanthony.
    Is your pressure transducer a Danfoss AKS 32R as is supplied here in Europe.

    I may be able to help but because of size details I will have to email them to you, rather than post them.

    It's relatively easy to test the Signal / voltages from them.
    Grizzly
    Gauge pressure for seq. suction and compressor suction gauge reading are pretty much dead on when in sequenced mode.M&M is telling us to keep in sequenced mode while we r using just 1 compressor but i always figured you use seq mode when running 2 compressors .

  13. #13
    Join Date
    Sep 2010
    Location
    United States
    Posts
    32
    Rep Power
    0

    Re: Suction values jumpin around

    Seq. mode removes each compressors micro panel reading and replaces it with the house reading. So they will all be reading the same suction pressures when staging on and off. Did you get the number I sent you?

  14. #14
    Join Date
    Sep 2010
    Location
    United States
    Posts
    32
    Rep Power
    0

    Re: Suction values jumpin around

    So yes, you would tend to use it when running multiple compressors or a trim compressor.

  15. #15
    Join Date
    Sep 2010
    Location
    United States
    Posts
    32
    Rep Power
    0

    Re: Suction values jumpin around

    Have you come any closer to solving your problem?

  16. #16
    Join Date
    Jan 2011
    Location
    GREECE
    Age
    51
    Posts
    8
    Rep Power
    0

    Re: Suction values jumpin around

    Chanche o rink in safety valve on comprecor

Similar Threads

  1. Copeland select 6
    By Copman in forum Tools and Calculators
    Replies: 9
    Last Post: 27-05-2010, 09:01 PM
  2. R290 Suction Scrubber HI Level
    By Knappyfro in forum Trouble Shooting
    Replies: 1
    Last Post: 28-11-2009, 05:15 PM
  3. Location of Suction Filter
    By Ray123 in forum Fundamentals
    Replies: 2
    Last Post: 11-06-2009, 03:29 PM
  4. Replies: 0
    Last Post: 14-05-2008, 05:05 PM
  5. Benji
    By benji in forum Trouble Shooting
    Replies: 29
    Last Post: 30-01-2008, 01:25 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •