    Daikin Ryn35cvmb7



    Been called to a Daikin split system on a server room previous engineer says compressor has gone but I'm not sure the unit is not in fault compressor just doesn't seem to be getting a start signal it's not down to earth it just doesn't wanna start not power to the compressor but power to condenser fan could it just be the pcb some internal fuse blown or something



  2. #2
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: Daikin Ryn35cvmb7

    hi kirky, you say , its not down to earth , have you tested the windings?
    sedgy,

  3. #3
    Join Date
    Jan 2011
    Location
    bg
    Age
    56
    Posts
    8
    Rep Power
    0

    Re: Daikin Ryn35cvmb7

    verification is easy. measure the resistance of the windings and the housing. appliance must have a range exceeding 2000k

  4. #4
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,853
    Rep Power
    46

    Re: Daikin Ryn35cvmb7

    Hi Kirky,

    Is it an inverter unit or does the compressor start dol?

    Any fault codes or flashy lights?

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: Daikin Ryn35cvmb7

    You say the fan runs, is there power to the contactor on the control side?

    Check the safety circuit.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Daikin Ryn35cvmb7

    On a side note, donuts Brian?

    Sorry to hijack
    The difference between genius and stupidity is that genius has its limits.

    Marc

  7. #7
    Join Date
    Aug 2009
    Location
    Manchester
    Posts
    179
    Rep Power
    15

    Re: Daikin Ryn35cvmb7

    Thanks for getting back to me. The unit isn't showing any fault lights the LED on the PCB is flashing away show normal conditions the condenser fan runs I've got power at the outdoor unit going into the PCB but no power onto the compressor it is not inverter driven. In the past when the compressor is faulty the compressor will at least try to start and usually take out the circuit breaker or pop a fuse but on this unit nothing happens am I wrong in thinking that if it was the windings that the compressor would at least try to start

  8. #8
    Join Date
    Aug 2009
    Location
    Manchester
    Posts
    179
    Rep Power
    15

    Re: Daikin Ryn35cvmb7

    Looks like the compressor is protected by a temp sensor mounted on the head of the compressor can't remember it's proper name a little rusty but it is wired directly into the pcb as is the comp and fan

  9. #9
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,853
    Rep Power
    46

    Re: Daikin Ryn35cvmb7

    Have you checked for voltage at the compressor terminals?

    If there is power then put your amp meter on the wire to the compressor and see if it is pulling any current, it could be seized but not burnt out, it will pull LRA for a few seconds then go to 0 for a few minutes and then repeat, it would keep doing this till the motor gets hot enough to short out and blow a fuse.

    If there is no power then check the wiring back to the board and then check the relay or contactor. It would be worth checking the capacitor too if its single phase.

  10. #10
    Join Date
    May 2006
    Location
    Isle of Wight, Uk
    Age
    47
    Posts
    424
    Rep Power
    20

    Re: Daikin Ryn35cvmb7

    Check the contactor, even if the coil is energised, doesn't mean the power is getting through, the contacts may be burnt out.

    Andy

  11. #11
    Join Date
    Aug 2009
    Location
    Manchester
    Posts
    179
    Rep Power
    15

    Re: Daikin Ryn35cvmb7

    There isn't any power at the compressor terminals it isn't even trying to start it's a very simple unit power directly into the pcb with everything else wired directly from the pcb. If I've got power into the pcb but not at the compressor terminals then it's gotta be the board maybe the capacitor gone or something I've dealt with faulty compressors in the past and they at least try to start but this one does nothing it doesn't throw the breaker

  12. #12
    Join Date
    Jan 2011
    Location
    bg
    Age
    56
    Posts
    8
    Rep Power
    0

    Re: Daikin Ryn35cvmb7

    if not go to the compressor voltage problem will Vrelo compressor on board

  13. #13
    Join Date
    Jan 2011
    Location
    bg
    Age
    56
    Posts
    8
    Rep Power
    0

    Re: Daikin Ryn35cvmb7

    if not go to the compressor voltage problem will be the compressor relay on board sorry

  14. #14
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: Daikin Ryn35cvmb7

    There must be a power relay on that board feeding power to the compressor, check power across the relay. Also bypass the relay to check if the compressor starts after having checking the motor windings.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  15. #15
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: Daikin Ryn35cvmb7

    Quote Originally Posted by marc5180 View Post
    On a side note, donuts Brian?

    Sorry to hijack
    OK, yup, just noticed; two virtual jam ones en route. (Damn, I hate people with long memories. )
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  16. #16
    Join Date
    Aug 2009
    Location
    Manchester
    Posts
    179
    Rep Power
    15

    Re: Daikin Ryn35cvmb7

    Cheers guys for all your help the unit is old and in pretty bad condition so we just gona replace full system. Someone had installed the condenser under a overflow pipe so the unit is soaked and covered in moss

  17. #17
    Join Date
    Feb 2007
    Location
    north west
    Age
    36
    Posts
    243
    Rep Power
    18

    Re: Daikin Ryn35cvmb7

    Quote Originally Posted by marc5180 View Post
    On a side note, donuts Brian?

    Sorry to hijack

    Trust you to be thinking of food again (curly chunk)
    ajj

Similar Threads

  1. Daikin not working... many problems
    By stankovicv in forum Air Conditioning
    Replies: 26
    Last Post: 11-12-2010, 09:01 AM
  2. Mitsi City Multi VS Daikin VRV
    By sumsor in forum Fundamentals
    Replies: 5
    Last Post: 14-07-2010, 05:54 PM
  3. Daikin, Why do we bother?
    By gwilliamson in forum Air Conditioning
    Replies: 21
    Last Post: 02-02-2010, 09:38 AM
  4. Daikin AC parts from UK
    By skel00 in forum Air Conditioning
    Replies: 5
    Last Post: 05-04-2009, 01:24 PM
  5. Fixing Daikin A3 Error
    By Stuffy in forum Air Conditioning
    Replies: 3
    Last Post: 27-03-2009, 06:02 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •