WIC outdoor condensing unit, Running High head in low ambient
Hi everyone! i got sent out to replace a semi-her. compressor 1hp run with R-22. After finished everything and start up the unit. my gauge reading 43psig for low side and 250psig for high side with the ambient temperature -20C (-4F). Temperature in the box is dropping and satisfied the T-stat. i'm thinking the head master might not working properly. but i'm not sure, would anyone able to help me out.
Thang
-
12-01-2011, 08:14 AM #2
Re: WIC outdoor condensing unit, Running High head in low ambient
And sight glass only 1/4 full. Running load amps rated 6.2A, and when i checked for running amperes, only 3.5A, properly low in charge, but compressor running high head that why i didn't add any more gas in. By the way the compressor had been re-built.
-
12-01-2011, 02:58 PM #3
Re: WIC outdoor condensing unit, Running High head in low ambient
Sounds like contaminants in the system to me, I would try reclaiming the refrigerant re- vacing the system and putting new gas in.
Roger
-
12-01-2011, 03:46 PM #4
Re: WIC outdoor condensing unit, Running High head in low ambient
Why did the original compressor need changing?
Is the condenser clean?
Did you also change the drier as well?
-
13-01-2011, 12:53 AM #5
Re: WIC outdoor condensing unit, Running High head in low ambient
Original compressor was open winding, took out to the shop to re-built and then i got sent out to replace. evacuated to 350 microns, new drier filter, recovered with filtered and re-use the refrigerant, acid test for refrigerant and oil, good. start up compressor, running with high head, and sight glass only showed 1/4 full. head master for r-22 minimum maintain pressure in low ambient 180psi. in this case i'm not sure, Roger Head might be right, contamination! i didn't have a chance to go back yet.
-
19-01-2011, 07:07 AM #6
Re: WIC outdoor condensing unit, Running High head in low ambient
I would also say you have contaminants. do what was sugested,evacuate system, use new reff, and hi capacity drier. I suspect the reff. was contaminated when it was removed and then used again..
Please let us know the out come. so we can all learn.
good luck.
-
19-01-2011, 09:10 AM #7
Re: WIC outdoor condensing unit, Running High head in low ambient
sounds like contaminets for sure
"Old fridgies never die, they just run out of gas!"
Similar Threads
-
MICROPROCESSOR DIAGNOSTICS/Differnces beteween TK/CTC
By REEFER-TEK in forum TransportReplies: 12Last Post: 27-03-2011, 04:12 AM -
Using Condesing unit and High load and temperature?
By evcelica in forum Technical DiscussionsReplies: 17Last Post: 19-10-2010, 04:41 PM -
3-door Hussman freezer - High head?
By W.ma.RefrigTech in forum Trouble ShootingReplies: 3Last Post: 21-03-2010, 09:32 AM -
Compressor loading, cooling, and range of operation.
By Air duster in forum FundamentalsReplies: 10Last Post: 02-04-2008, 08:39 AM -
TK basic micro-p features and functions
By REEFER-TEK in forum TransportReplies: 0Last Post: 05-12-2007, 06:25 PM