    Exclamation WIC outdoor condensing unit, Running High head in low ambient



    Hi everyone! i got sent out to replace a semi-her. compressor 1hp run with R-22. After finished everything and start up the unit. my gauge reading 43psig for low side and 250psig for high side with the ambient temperature -20C (-4F). Temperature in the box is dropping and satisfied the T-stat. i'm thinking the head master might not working properly. but i'm not sure, would anyone able to help me out.

    Thang



  2. #2
    thangbom's Avatar
    thangbom Guest

    Re: WIC outdoor condensing unit, Running High head in low ambient

    And sight glass only 1/4 full. Running load amps rated 6.2A, and when i checked for running amperes, only 3.5A, properly low in charge, but compressor running high head that why i didn't add any more gas in. By the way the compressor had been re-built.

  3. #3
    Join Date
    May 2005
    Location
    newbury
    Age
    44
    Posts
    13
    Rep Power
    0

    Re: WIC outdoor condensing unit, Running High head in low ambient

    Sounds like contaminants in the system to me, I would try reclaiming the refrigerant re- vacing the system and putting new gas in.
    Roger

  4. #4
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: WIC outdoor condensing unit, Running High head in low ambient

    Why did the original compressor need changing?

    Is the condenser clean?

    Did you also change the drier as well?

  5. #5
    thangbom's Avatar
    thangbom Guest

    Re: WIC outdoor condensing unit, Running High head in low ambient

    Original compressor was open winding, took out to the shop to re-built and then i got sent out to replace. evacuated to 350 microns, new drier filter, recovered with filtered and re-use the refrigerant, acid test for refrigerant and oil, good. start up compressor, running with high head, and sight glass only showed 1/4 full. head master for r-22 minimum maintain pressure in low ambient 180psi. in this case i'm not sure, Roger Head might be right, contamination! i didn't have a chance to go back yet.

  6. #6
    Join Date
    Jun 2010
    Location
    Oregon
    Posts
    20
    Rep Power
    0

    Re: WIC outdoor condensing unit, Running High head in low ambient

    I would also say you have contaminants. do what was sugested,evacuate system, use new reff, and hi capacity drier. I suspect the reff. was contaminated when it was removed and then used again..
    Please let us know the out come. so we can all learn.
    good luck.

  7. #7
    Join Date
    Nov 2003
    Location
    NSW, Australia
    Age
    40
    Posts
    242
    Rep Power
    21

    Re: WIC outdoor condensing unit, Running High head in low ambient

    sounds like contaminets for sure
    "Old fridgies never die, they just run out of gas!"

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. Using Condesing unit and High load and temperature?
    By evcelica in forum Technical Discussions
    Replies: 17
    Last Post: 19-10-2010, 04:41 PM
  3. 3-door Hussman freezer - High head?
    By W.ma.RefrigTech in forum Trouble Shooting
    Replies: 3
    Last Post: 21-03-2010, 09:32 AM
  4. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  5. TK basic micro-p features and functions
    By REEFER-TEK in forum Transport
    Replies: 0
    Last Post: 05-12-2007, 06:25 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •