    mitsubishi heavy industry problem



    hi

    going to a job this week someones already been and they said two units on the systam aint heating,the system is a misubishi heavy industry 3 pipe system each unit has its own bs box i was thinking short of gas or solinoid valve in bs box as gone,if anyones got any ideas thanks



  2. #2
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,120
    Rep Power
    25

    Re: mitsubishi heavy industry problem

    First things first ,do they operate in cool mode , is the eev in the indoor ok.A system that is short of gas will usually experience a loss of duty across the board if all units are operating under the same mode.Turn off the other units and run the two suspects on their own to see how they go .
    Check the control wiring and solenoids at branch selectors if the above ideas come up short..
    Cheers
    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

Similar Threads

  1. Replies: 1
    Last Post: 07-03-2010, 01:09 PM
  2. mitsubishi heavy industries fault
    By skeggyboy in forum Air Conditioning
    Replies: 3
    Last Post: 20-08-2009, 06:41 PM
  3. Few question about Mitsubishi Heavy Industrial air condition
    By fireduck in forum Air Conditioning
    Replies: 55
    Last Post: 12-05-2009, 02:35 PM
  4. Mitsubishi HI KX4 140 problem
    By gwilliamson in forum Air Conditioning
    Replies: 30
    Last Post: 21-12-2008, 11:54 AM
  5. Mitsubishi VRF Problem
    By Freecool in forum Heat Pumps
    Replies: 1
    Last Post: 02-11-2007, 11:02 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •