    Leaving conditions of DX HELP REQUIRED!!!



    Hi

    One of enquiries came to me with data as under

    Entering DB/WB(F) 104/83
    CFM 1200
    Capacity 53 MBH

    Now I want to design the DX coil Please tell me what will be leaving dry bulb/wet bulb (capacity=4.5xCFMx enthalpy difference) what will be RH of leaving air and how we can draw it on psychometric chartMoreover what will be evaporating temperature?


    Our nose is our personal air-conditioning system: it warms cold air, cools hot air and filters impurities

  2. #2
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Leaving conditions of DX HELP REQUIRED!!!

    This can only be determined with a practical test.
    You have at first the bypass factor, the capacity will also vary if ripple fine tubes are used, flat fins of preformed fins to increase turbulence between the fins, if tubes are positioned in line or in an X-pattern, injection pattern,...

    What I do is measure an excisting coil and look in the catalogue what capacity the manufacturer gives.
    This gives a very accurate estimate of it.

    Or run a simulation program of a manufacturer and look what size of coil it calculates.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  3. #3
    Join Date
    Jun 2005
    Location
    California
    Posts
    394
    Rep Power
    19

    Question Re: Leaving conditions of DX HELP REQUIRED!!!

    To find the enthalpy difference is 4.5 x 1200 cfm x (h1-h2) = 53,000 btu/hr or (h1-h2) = 53,000/5400 = 9.815 btu/lb air
    So if 104*f and 83*f WB = Enthalpy 46.764 btu/lb – 9.815 btu/lb = Enthalpy 36.949 btu/lb final condition.
    Now working this out on my trusty abacus I get the following final conditions
    DB = 74*F
    WB 73.279*F
    RH = 96.7*F
    DP = 73.01*F This is air off ADP ~ 72*f
    122.78 = moisture content
    13.712 = SV
    36.949 = enthalpy
    The sensible heat = lbs air x 0.24 x TD = 87.51lbs x 0.24 x 30*F x 60 min = 37,806 btu/hr.
    The latent heat = 138.12 gr/lb-122.78gr/lb = 15.34gr/lb x 87.51lb/air = 1342btu/min x 60min = 80,545gr/hr devided by 7000gr/lb = 11.5lbs/hr x 970btu/lb = 11,161btu of latent heat
    Total heat = 37,806+11,161 = 48,967 btu. So the SHF is 11,161/48,967 = ~ 77%
    I estimated a by pass factor ~ 10%
    To prove maybe you should run a test

  4. #4
    Join Date
    Dec 2004
    Location
    Weihai,China
    Posts
    800
    Rep Power
    20

    Re: Leaving conditions of DX HELP REQUIRED!!!

    Hi wambat,
    What formula your calculation based on ?It depends on the DX coil paremeters. I don't understand how you estimate. Pls give some explanation. thx!

    rgds
    LC

  5. #5
    Join Date
    Jun 2005
    Location
    California
    Posts
    394
    Rep Power
    19

    Re: Leaving conditions of DX HELP REQUIRED!!!

    Ic-Shi the parameters were given as 1200 CFM, 53000 BTUS, 104*F, and 83*F WB so if you use the formula Q = 4.5 x CFM x (h1-h2) you get 4.5 x CFM x (H1-H2) = 53000 Btu's. So I need to find (h1-h2) and that’s = to 53,000 btu/4.5x1200 = 53,000 btu/5400 = 9.815 btu/lb of air. So if I determine what h1 is by the parameters given and subtract 9.815 btu from it I then know what h2 should be, once I know this I know what the final enthalpy is, when I know what the final enthalpy is I can find the final air conditions

  6. #6
    Join Date
    Dec 2004
    Location
    Weihai,China
    Posts
    800
    Rep Power
    20

    Re: Leaving conditions of DX HELP REQUIRED!!!

    Oh yeah. I see. But you supposed the coil is properly designed. Actually the Q is changeable according to the actual heat transfer performance of the coil. However it could be used by estimation-

    thx.
    LC

  7. #7
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Leaving conditions of DX HELP REQUIRED!!!

    I agree your psychometrics Wambat but what are now the actual dimensions of the coil given that we need to evaporate at 0°C/32F?
    What velocity will you use?
    And how to determine how many rows, tube diameter, injection pattern...
    These can't be calculated.

    I think that was the underlaying question of Abbasi.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  8. #8
    Join Date
    Apr 2004
    Location
    Pakistan
    Age
    44
    Posts
    129
    Rep Power
    21

    Re: Leaving conditions of DX HELP REQUIRED!!!

    I will second with PETER


    WAMBAT

    we all know Sensible heat= 1.08 x cfm x Temp difference

    Here u calculated 38000BTU/hr

    addin bypass factor in above and subtractin from total gives latent heat. thats basic thermodynamics.

    But mate question is how to select evaporating temperature without it no DX coil in world may be designed

    also how can u guess RH of leaving air?

    we can all calculate wet bulb what about dry bulb

    again i wud repeat my question and it is

    "what will be evaporating temperature?
    and Dry bulb of leaving can u calculate these by drawing on psychometric chart?
    what is criteria for choosing evaporating temperature in relation to leaving DB/WB?"


    Its a question that i have been trying to find out for somewhile now. I will appreciate if someone comes up with some clue about it
    Our nose is our personal air-conditioning system: it warms cold air, cools hot air and filters impurities

  9. #9
    Join Date
    Dec 2004
    Location
    Weihai,China
    Posts
    800
    Rep Power
    20

    Re: Leaving conditions of DX HELP REQUIRED!!!

    abb,
    Based on your data,the leaving air DB/WB can be decided by capacity=air volume*dh formula. As for evaporation temp ,there are more than one solutions which depend on the coil paremeters(rows/FPI/face area/refrigerant type etc). The equation Q=K*LMt is not a linear equation which need trial calcualtion to get the optimal solution.
    I don't think the leaving point can be directly draw by pschrometric chart because the out air decided by coil characteristics.

    rgds
    LC

Similar Threads

  1. Replies: 3
    Last Post: 06-11-2006, 05:04 AM
  2. Chart for the "whys of conditions?
    By frankiee in forum Fundamentals
    Replies: 5
    Last Post: 30-04-2006, 09:26 PM
  3. Required Control Wiring 50dp-020-910 Carrier
    By altaf22m in forum Air Conditioning
    Replies: 2
    Last Post: 08-08-2005, 06:08 PM
  4. Replies: 4
    Last Post: 10-06-2005, 12:25 AM
  5. Power required in a compressor
    By Friobernal in forum Fundamentals
    Replies: 3
    Last Post: 06-02-2003, 02:21 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •