    Hi Guys,
    I have a problem with a Recip York Chiller. Everytime I reset the chiller it show on the display a "Motor Current" on both System before the compressor even start.
    Any one can help?
    Thanks



  2. #2
    Join Date
    Mar 2005
    Location
    u.a.e
    Age
    68
    Posts
    169
    Rep Power
    20

    Re: York Chiller

    Check the external H.P cut out switch and its wiring circuit, If that is open the same fault shows at display.

  3. #3
    Join Date
    Jul 2005
    Location
    France- USA
    Age
    47
    Posts
    27
    Rep Power
    0

    Re: York Chiller

    What type of control do you have, was it built by York Basildon ?

    Regards

    Julien

  4. #4
    Join Date
    Aug 2005
    Location
    USA
    Age
    59
    Posts
    25
    Rep Power
    0

    Re: York Chiller

    What value is the unti showing and also does this happen just before the compressor starts?

  5. #5
    Join Date
    Mar 2005
    Location
    u.a.e
    Age
    68
    Posts
    169
    Rep Power
    20

    Re: York Chiller

    RubinJLL
    Did your YORK comes on line?

  6. #6
    Join Date
    Sep 2005
    Location
    Hampshire
    Age
    43
    Posts
    16
    Rep Power
    0

    Re: York Chiller

    What sort of controller is it using gold standard or gold standard intelligent, the latter is a micro-processor with key pad

  7. #7
    Join Date
    May 2004
    Location
    england
    Age
    61
    Posts
    48
    Rep Power
    0

    Re: York Chiller

    it may just require recalibrating. on commisioning, some york chillers have to be calibrated eg. slide valve settings and % motor overcurrent. motor current will generate an alarm before it even starts.

  8. #8
    Join Date
    Jul 2004
    Location
    england
    Age
    52
    Posts
    64
    Rep Power
    20

    Thumbs up Re: York Chiller

    Check on the Pcb board for two red lights its in the top right hand corner. This is for the thermistor on compressor. You might have a fault on the hp switch. Very common problem with the screw chillers.

  9. #9
    Join Date
    Jul 2005
    Location
    INDIA
    Age
    51
    Posts
    14
    Rep Power
    0

    Re: York Chiller

    check ur compressor protector module which is fixed inside the terminal cover of compresor. it might be defective. if possible replaced the CP MODULE and check, possible it will work normally. ALSO, check compressor toroid i.e(current transformer) ohms, it should be around 65 ohms. GOODLUCK.

  10. #10
    Join Date
    Dec 2005
    Location
    Zagreb
    Posts
    190
    Rep Power
    19

    Thumbs down Re: York Chiller

    You have big problem and the owner of this chiller even bigher.

  11. #11
    Join Date
    Dec 2005
    Location
    uae
    Posts
    54
    Rep Power
    19

    Re: York Chiller

    Hi,
    check or replace the relay out put board and you can check the moisture inside the compressor terminal box.then clean it.

  12. #12
    Join Date
    Jul 2007
    Location
    singapore
    Posts
    18
    Rep Power
    0

    Re: York Chiller

    HI,WHAT IS UR MODEL OF UR CHILLER? if ur model is YEAJ series check the analog input j plug voltage at microboard when stand by must be 0.5 volt dc, when it run it shoulld start from 1.4voltdc,when it load it may rise untill 1.9 volt dc if it is not ur micro board to be replace need any help i can help u i am working in york almost 7years thanks

  13. #13
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,261
    Rep Power
    31

    Re: York Chiller

    Hi, RubenJLL

    Quote Originally Posted by RubenJLL View Post
    Hi Guys,
    I have a problem with a Recip York Chiller. Everytime I reset the chiller it show on the display a "Motor Current" on both System before the compressor even start.
    Any one can help?
    Thanks
    This can be if emergency button is not released or has some internal wiring wrong...

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  14. #14
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Thumbs up Re: York Chiller

    Rubenjll.
    I suspect there are enough engineers out there to resolve your dilemma. But we need a little more detail.
    1 valuable method of narrowing fault diagnosis down is to:-
    Enter the History menu and read the data therein!
    ie High HP would show a high hp reading at the time of cut out. Whereas you would expect to see possibly a high Motor FLA. On a "Motor Current".
    Many things can be acertained from interigateing the system history.
    For instance if the system runtime D.Hrs.Mins. & Seconds shows 0.0.0.3 its pretty resonable to discount a motor overload. But you might deside to
    check that the motor is switching from "star" to "delta" etc.etc.
    Thats assuming that the motor is star delta and not part wind.
    The history buffer is very valuable in determining whats been happening and if you have the facility you can print of a hardcopy.
    Very USEFULL especially as York systems only record the last 3 or 6 events (faults).
    You would have to reset both systems after a "motor current" shutdown. I assume you have been doing that.
    As many before me have tried to explain there are a lot of possible reasons for this fault and without knowing the model conserned it's very difficult to narrow the fault further.
    May I ask could you let us all know how this develops, A lot of the time we are left wondering as to wether we have been of assistance.
    I must point out that a lot of York kit is different
    in Europe to the America's.
    The fundermentals are the same though.
    Grizzly

  15. #15
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: York Chiller

    Check the dates fellas, it's over two years old

    Also the guy never came back to us again, another one-poster
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  16. #16
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Thumbs up Re: York Chiller

    Now I know why you are a moderator Brian!
    You actually read everything properly before replying
    Grizzly.
    Hopefully someone will benifit from my explanation?

  17. #17
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: York Chiller

    Oh yes, someone always benefits that's for sure.

    To be honest sometimes these 'semi-dead' threads come alive again because no-one knew the answers first time around and, as usual, a fresh mind kick starts it again.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  18. #18
    Join Date
    Jul 2007
    Location
    singapore
    Posts
    18
    Rep Power
    0

    Re: York Chiller

    Hi,any Body Can Help To Send York Ycam Model Air Colled Chiller Wiring Digram Or Which Web Site I Can Down Load

  19. #19
    Join Date
    Jan 2008
    Location
    Kent UK
    Age
    49
    Posts
    514
    Rep Power
    18

    Re: York Chiller

    Hi RAVISEKAR

    I think this is what you require

    http://www.yorkromania.ro/docum/Pc014_gb.pdf

    Hope it is
    If it ain't broke, it doesn't have enough features yet.


    Damo

  20. #20
    Join Date
    Jul 2007
    Location
    Czech
    Age
    61
    Posts
    373
    Rep Power
    18

    Re: York Chiller

    Hi RAVISEKAR,
    and number?

  21. #21
    Join Date
    Jul 2007
    Location
    singapore
    Posts
    18
    Rep Power
    0

    Re: York Chiller

    Thanks Chunk,my Model Number Is Ycam 300 Four Comprassor With Master And Slave Panel With Refcomp Compressor

Similar Threads

  1. York Chiller
    By HVACGod in forum Commercial
    Replies: 12
    Last Post: 11-09-2010, 06:05 AM
  2. York Chiller
    By tomt in forum Commercial
    Replies: 1
    Last Post: 05-12-2007, 11:24 AM
  3. York Screw Chiller How low will it go?????
    By bruceboldy in forum Industrial Compressors
    Replies: 11
    Last Post: 10-08-2007, 10:29 PM
  4. york chiller not running
    By cool it in forum Trouble Shooting
    Replies: 21
    Last Post: 16-06-2006, 12:13 AM
  5. York process chiller repairs
    By Matt in forum Commercial
    Replies: 5
    Last Post: 23-03-2004, 11:07 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •