07-01-2011, 09:35 AM #1
External Static Pressure Calculations
hello everyone and thank you all .. this forum helped me alot ... and this is my first post.
sometimes and sadly there is no time to make a proper ESP calculation, if using the regular constant fiction method for duct sizing ... what would be the disadvanages of oversizing the external static pressure of the AHU fan ?
thank you.
Shadi
07-01-2011, 11:21 AM #2
Re: External Static Pressure Calculations
Only the dogmatist says he will never change his mind. We all know that some of our opinions are wrong but none of us know which they are for if we did then they just wouldn't be our opinions. - JS Mill.
07-01-2011, 10:30 PM #3
Disadvantage would be excessive energy usage.
08-01-2011, 12:53 AM #4
Are you talking about trunk duct design, static re-gain method.
08-01-2011, 12:58 AM #5
08-01-2011, 04:54 AM #6
Both in AHU and pumps excess static and head in pumps is always an issue not given due importance consequently energy wastage. Ideally as soon as commissioned the Air quantity shall be measured and if need be pulley of motor is changed along with belts so as to deliver closer to design air quantity so that the system will be effective. Then adding VFD will save further power .
Superheat and Subcooling
York YPAL095 static pressure troubles
By Triggerman in forum Air ConditioningReplies: 1Last Post: 19-07-2010, 09:57 PM -
By nr1990 in forum RefrigerantsReplies: 1Last Post: 05-07-2010, 11:34 PM -
By Derek in forum RefrigerantsReplies: 3Last Post: 04-10-2001, 01:50 PM